Hi, i have a ring main with 6 sockets 32a breaker 2.5mm/1.5mmcpc for which i am getting a reading of 0.38 IR between L-E, how do i go about finding the fault
Also i have a shower 40a breaker 6mm/2.5cpc with a reading of 0.26 IR between L-N, how do i go about finding the fault.

This question is part of my assessment at college and any tips, offers of help would be very much appreciated
Thank you :))
 
The normal fault finding method on a ring final circuit is split the ring. As this is a college assement I have to assume that all loads have been romoved. You would normally find the approx middle of the ring and remove the socket and divide the legs up into the 2 legs. You do another IR test and it will show you which leg the fault is on, you then just remove each socket and split the cables until you get the poor reading.

On the shower you would normally open the double pole switch and IR the cable from the CU to switch if that is OK. You then drop the switch and disconnect the shower and and test the cable from switch to shower, if that cable is OK you know it is the shower, are they wanting you to test the shower??

Must remember as this is an assement you must make sure you do everything by the book, safe isolation, checking the meter and probes for damage etc etc.

I have to ask those readings are really really low nearly a dead fault, you sure it is IR and not part of a ring continuity test or a R1 +R2.
 
the 0.38, i assume is 0.38 Mohms. check all sockets for a possible faulf behind socket, trapped cable etc. check for junction boxes under floors. try and get a reading with the sockets pulled off the walls.

your 0.26 on the shower may well be the shower itself. to get an accurate reading you need to dis. the cable in the shower. also, it could be the neon in the shower switch.
 
Hi Malcolm, thanks for your help - to answer your question i has readings of 0.5 as R1+R2 but rn was oc, does this make sense?

Thanks Telectrix, would the neon cause the reading to be so low?

Also if i have a faulty switch on a 2way circuit, do i try to identify and label ends to work out one of the cables as faulty?
 
if rn is o/c you will still read IR and also r1+r2. if this is college work, it's likely that a N has been dissed behing a socket.
 

Reply to A little help with 2 IR readings please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top