righto chaps and chappesses, I'm currently devising a spreadsheet to calculate the cable size needed for various sizes of cable for use on the DC circuits of commercial jobs where the DC voltage cable be 6-800V.
The reason being that a different spark has reported that an SWA cable we'd installed on a job a while back was running quite warm, and tbh I think we did the cable calcs on the job and I don't have a record for them, but as far as I could work out it ought to have been well inside the ratings... though having checked I see the ratings are for up to 90 deg C cable temp, so it could well be running warm even if inside the spec.
Anyway, one point that's confusing me is that the latest version of the solar installers guide says we need to work out the current carry capacity based on the Isc according to the requirements of BS7671 etc.
But in my head, I just can't get away from thinking that we ought really to be converting all this to watts, as surely we need to be taking account of the fact that while a single string circuit will only be carrying a current of around 8 amps, it's carrying that current at say 600V, meaning that it's carrying 4.8kW vs 1.8kW for an 8 amp 230V AC circuit.
So the way I've got the spreadsheet set up is to convert the ratings of the cables in BS7671 into an equivalent power rating in kW, then applied the derating factors etc, then compare the peak kW rating of the DC circuit.
If none of this matters and it really is just the current that matters, then fair enough, that makes things simpe, apart from the fact that it wouldn't even come close to explaining why I'm getting reports of a warm cable when the cable is 6mm2 carrying at most 16 amps (ok clipped direct SWA 4 core, possibly in direct sunlight, but even so it's still only 50% of the rated current for the cable in amps)
So can anyone clarify this for me, as to whether we should just be using the Isc figures in amps and ignoring the fact that it's running at 600V and therefore 2.5 x the actual power, as would be implied by the guidance, or am I right in thinking we should be accounting for the increased power flowing through the cable and doing the calcs in watts?
Sorry if this seems a bit basic, I'm just driving myself a wee bit made here trying to get my head around it, so a little assistance would be appreciated.
ps once I've sorted the spreadsheet, I don't mind posting it up for comment / others to use, as long as I've got it right.
The reason being that a different spark has reported that an SWA cable we'd installed on a job a while back was running quite warm, and tbh I think we did the cable calcs on the job and I don't have a record for them, but as far as I could work out it ought to have been well inside the ratings... though having checked I see the ratings are for up to 90 deg C cable temp, so it could well be running warm even if inside the spec.
Anyway, one point that's confusing me is that the latest version of the solar installers guide says we need to work out the current carry capacity based on the Isc according to the requirements of BS7671 etc.
But in my head, I just can't get away from thinking that we ought really to be converting all this to watts, as surely we need to be taking account of the fact that while a single string circuit will only be carrying a current of around 8 amps, it's carrying that current at say 600V, meaning that it's carrying 4.8kW vs 1.8kW for an 8 amp 230V AC circuit.
So the way I've got the spreadsheet set up is to convert the ratings of the cables in BS7671 into an equivalent power rating in kW, then applied the derating factors etc, then compare the peak kW rating of the DC circuit.
If none of this matters and it really is just the current that matters, then fair enough, that makes things simpe, apart from the fact that it wouldn't even come close to explaining why I'm getting reports of a warm cable when the cable is 6mm2 carrying at most 16 amps (ok clipped direct SWA 4 core, possibly in direct sunlight, but even so it's still only 50% of the rated current for the cable in amps)
So can anyone clarify this for me, as to whether we should just be using the Isc figures in amps and ignoring the fact that it's running at 600V and therefore 2.5 x the actual power, as would be implied by the guidance, or am I right in thinking we should be accounting for the increased power flowing through the cable and doing the calcs in watts?
Sorry if this seems a bit basic, I'm just driving myself a wee bit made here trying to get my head around it, so a little assistance would be appreciated.
ps once I've sorted the spreadsheet, I don't mind posting it up for comment / others to use, as long as I've got it right.