Hi I was on internet and noticed this question (its not my question) which seem quite unusual and just wondered what you guys thought of this situation. I notice the reply to the question did not answer the question. I cant see anything wrong......
Subcategory - 1. BS7671
Question
I was doing some work for a client the other week and upon going upstairs, noticed a 45A cooker switch/socket outlet adjacent to the bathroom door. When I enquired as to why it was there, my client said it was the shower switch and a socket for her hairdryer as she didn't have a socket on the landing. Which got me thinking if this was entirely appropriate.
The shower circuit was wired in 10.00mm T&E with 50A MCB and 100A 30mA RCD with the label 'Shower and socket on landing'. The shower is 9.5Kw and the board is 3 / 5 way split load.
Answer
BS 7671:2008 allows a socket outlet within the bathroom to be fitted provided it is 3m from the boundary of zone 1 and must be protected by a 30mA RCD.
A 10mm cable can carry 52Amps (from table 4D2A) if the cable is installed within a building void without insulation. Table 4D5 gives current carrying capacities of cables covered with insulation.
Regards
Subcategory - 1. BS7671
Question
I was doing some work for a client the other week and upon going upstairs, noticed a 45A cooker switch/socket outlet adjacent to the bathroom door. When I enquired as to why it was there, my client said it was the shower switch and a socket for her hairdryer as she didn't have a socket on the landing. Which got me thinking if this was entirely appropriate.
The shower circuit was wired in 10.00mm T&E with 50A MCB and 100A 30mA RCD with the label 'Shower and socket on landing'. The shower is 9.5Kw and the board is 3 / 5 way split load.
Answer
BS 7671:2008 allows a socket outlet within the bathroom to be fitted provided it is 3m from the boundary of zone 1 and must be protected by a 30mA RCD.
A 10mm cable can carry 52Amps (from table 4D2A) if the cable is installed within a building void without insulation. Table 4D5 gives current carrying capacities of cables covered with insulation.
Regards