Thought I'd share this with you today.
Went to a customers house who after coming back from his holidays had a leak in the bathroom and spread to the airing cupboard.
On having this leak it's made all the water pipes in the property live. So customer disconnected immersion circuit at the fuse and I come round.
IR the circuit, get poor reading of 0.43 N-E. Looks like water damage in the wall. But why didn't the fuse blow when he got a shock? No RCD, support bonding non-existent in bathroom but present in airing cupboard.
Go downstairs to main bonding conductor under sink, do a continuity between disconnected bonding conductor at both ends of the run and find that the conductor which can be no more than a 1.5m has a reading of 1.05ohms. Hmm its seems the bonding was so old and corroded under the sink it wasn't allowing enough fault current to flow to blow the fuse. So always check the 0.05ohms reading regardless of length because you never know.
Can't go behind the walls just yet as it housing association.
 
The bonding I saw was a 6mm then, from MET to stop cock in kitchen BS 951 clamp with the 6mm in. Just did a continuity check and got a reading of .80ohms for a piece of cable maximum 12 metres. There for an hour checking connections re testing, test with cable on ,cable off and then fit new clamp just in case, finally told the customer that IMO there is something wrong it needs changing, but was run under floor. He told me that he was renovating the kitchen in a few weeks, so I ran a surface cable temp and came back.

Lifted the floor and found the 6mm going under from MET then a piece of bell wire twisted onto it run the length in bell wire, then out to stop cock in 6mm, but that leg was in a choc block ..........
 
Coming back to BS 951 .... stopped off in Screwfix today to pick up some clamps to do a spot of supp bonding. On the counter they had Tenby 'Rpaid Clamp Ultra'. I don;t know if these have been around for ages, and I've just missed them - did a search on Forum just now, but didn't find any mention.

Anyway, I asked how much and I think it was something like ÂŁ35 for a bag of 20 for 15mm pipes. Ha-ha-ha, yeah, no thanks, I'll take the usual please ...

So I was putting supplementary bonding on the pipework around imm tank in an airing cupboard - using the cheapo clamps. First one on no problem, then the clamp I'd attached to the other end of the bond fell apart while I was attaching it. To cut a long story a little bit shorter, I ended up messing around with this crappy things for best part of 10 minutes sweating away because of heat from tank. Stood back to admire my handywork then spotted in my frustration I'd securely attached it to the same bit of pipe as first clamp.

This new clamp had A-E on it - I'd like to take the designer to A+E.

So next time I'm in screwloose ... In case you haven't seen them ... http://www.legrand.co.uk/en/en/liblocal/pdf/Tenby Rapid Clamp Ultra DL.pdf
 
They are very useful, especially where access is poor - you can connect the cable before putting them on the pipe.

The label is moulded into the side of the plastic cover.

I buy mine singly from Edmundsons.
 
Correct, the 'do not disconnect .. ' is printed into the side - not very visible, but anyone who's going to disconnect a piece of Y-G cable that is obviouslypart of the electrical installation is going to do it anyway, IMO. Having tried the sample in the shop I can confirm it takes only a couple of seconds to attach clamp to pipe. Shame you need to different sizes for 15mm and 22mm, but I guess that would be stretching the design a bit to have one clamp do both.
 
So gents let's see if anyone can help me on this one. Same property, have yet to go back and do any work. When I left the first day I left the guy with an alternative. His two immersions where on plug top plugged into immersion circuit. I told him when I rewire the circuit these will be hard-wired in. So I put them on an extension and plugged it into the main ring so he can have hot water. Got a call couple days later saying he's tried it for 10 hours, no hot water.
Plumber got sent today to change immersions. Same thing, changes them over and starts working (can hear it in the cillender) them stops. Plumbers on the phone to me, continuity of 20 ohms on the immersions, power to it still not working with two new elements. Any idea lads? I'm sure it's got something to do with it still flowing to earth but can't figure of the pieces, any help?
Many thanks
 
If they started working and then just stopped surely it as got to be a thermostat/timer problem if there is power going to the elements.

With the elements in the non working mode, is there power to the thermostat ? If there is power to the thermostat then is there power on the supply side of the thermostat?

Not too sure. I'm going over tonight so that will be checked.
It's also turned out they are still getting shocks off the pipe work.
My theory is- the water damage has damaged the immersion flex causing a live to earth fault as this is the only part of the new immersion that has been reused. So when I get there IR the flexes. But my reason for that theory won't work is that BOTH immersions don't work.
 

Reply to A story of bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

D
  • Article
DHW supply from Vaillant turbomax 828e Hi, We have a combi boiler supplying dhw and c/h to our 4 bed, 2 bath house. The boiler is in a cupboard...
Replies
0
Views
173
diddlepara
D
P
  • Article
Smelly Odour Randomly Started I have had a mystery smell start in my house all of a sudden. The smell is prominent in an adjoining linen closet to...
Replies
0
Views
165
PlumbingNoob
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top