Just doing some certificates and noticed two minor works for one bathroom job. One for shower replacement with new switch, one for light and lv fan. Part P certs both exactly the same,'circuit alteration or addition in special location'. Do I need to send two? Just a thought rather than a prob. Cheers. Ian.
 
Do you mean two notifications? As two circuits have been altered then two minor works certificates will be required however only one notification would have to be made to the LABC which would detail both aspects of the job.
 
Thanks gents,as I thought. I've only notified once. But notifying requires certificate number (two certificates).Just a point.
 
Thanks gents,as I thought. I've only notified once. But notifying requires certificate number (two certificates).Just a point.

I can never be bothered to input the cert no. on the notification website, it's not mandatory anyway since it lets you submit without it.
 
I can never be bothered to input the cert no. on the notification website, it's not mandatory anyway since it lets you submit without it.

Thanks Dunc, that's that sorted.
 
My certificates use the same number as the invoice for the job. If there's more than 1 certificate I use xxxxxxx/A, xxxxxx/B etc
 

Reply to a very Minor problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

  • Question
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge...
Replies
14
Views
2K
It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
561

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top