Why is an A1 ring final circuit only protected by a 30/32A breaker when the max current carrying capacity of a 2.5 cable is 27A? (page 134 of OSG, column 6). Apologies in advance if I'm missing something very obvious. Thank you
 
Me thinks the reason why it is protected by a 30/32 fuse or cb is a thing called ohms law ie on a ring half the current flows down one leg and the other half down the other leg so max current on each leg is 16 amps but dont worry I think in 10 years the ring will be phased out because that and the 13 amp socket is all there is left to harmonise
 
Gustav would be turning in his grave if he read that!:disguise:

its correct in the simplest form without explaining that the ring acts like two radials but the load (because of the ring) in each direction is half the total and because of this a cable with a smaller csa can be used, but as we know this depends on equal loading on the ring which is near impossible so sometimes it may be practical to use a cable with a larger csa. Happy now lenny or are you going to read threads and post useless comments without actually contributing any information?? and perhaps youd like to know that the ring circuit came into effect to save the use of copper after world war 2 when rebuilding the cities enough info now?
.
 
its correct in the simplest form without explaining that the ring acts like two radials but the load (because of the ring) in each direction is half the total and because of this a cable with a smaller csa can be used, but as we know this depends on equal loading on the ring which is near impossible so sometimes it may be practical to use a cable with a larger csa. Happy now lenny or are you going to read threads and post useless comments without actually contributing any information?? and perhaps youd like to know that the ring circuit came into effect to save the use of copper after world war 2 when rebuilding the cities enough info now?
.

Not at all, not if the FRC is wired in a staggered ring configuration, the load will be relatively balanced!!

Oh, and the copper saving was only a part of the reasoning behind the FRC, this is a common miss-conception and mainly banded about by those that want to see the demise of the FRC, usually by inexperienced electricians that can't fault find on them!!
 
its correct in the simplest form without explaining that the ring acts like two radials but the load (because of the ring) in each direction is half the total and because of this a cable with a smaller csa can be used, but as we know this depends on equal loading on the ring which is near impossible so sometimes it may be practical to use a cable with a larger csa. Happy now lenny or are you going to read threads and post useless comments without actually contributing any information?? and perhaps youd like to know that the ring circuit came into effect to save the use of copper after world war 2 when rebuilding the cities enough info now?
.


If you have a read of my 9,400 other posts you will see how much useful info I share with the entire forum.

It's only when I see the unguided posting inaccuracies that may confuse other members that I raise questions on it, simply to make sure that correct info is then given.

One other thing, please don't proceed to lecture me in the history of the R.F.C, google isn't always accurate.:icon6:
 

Reply to A1 ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top