S
Sparkattack
Was asked to look at a fault with a pump that had been reported to have tripped a couple of times over the last few weeks. The setup is a ABB ACS 141 inverter drive(230Va.c) wired to a 2.2KW 1phase/3 phase motor, wired in delta at the motor 220v/240v supply. The pump ran up ok if not sounding a little rough! I firstly tested the motor and windings are balanced 2.25ohms, i then proceeded to check voltages. Drive input 230Va.c, but tested output at motor terminals between 180V to 200V? At this point the drive was only running at about 23Hz, clamp meter showed 3.4amps. This drop in voltage at the output suggests to me an issue with the drive. I then checked pump 2 which is identical setup to try and confirm this but that pump also tested out the same? Is there something I am missing? I'm convinced its a drive issue but its strange that both drives are the same!