i have been asked to pv quote for a barn which is 100 meters away, there is a 16mm cable running down to the barn,
my question is according to the sma software the voltage drop is 3.74v the power loss is 63 Watts

is this ok, i know the dti says you should try and keep the voltage drop below 1% but what if it is not possible
 
i have been asked to pv quote for a barn which is 100 meters away, there is a 16mm cable running down to the barn,
my question is according to the sma software the voltage drop is 3.74v the power loss is 63 Watts

is this ok, i know the dti says you should try and keep the voltage drop below 1% but what if it is not possible

It will result in the generation meter not recording some generation. The inverter possibly cutting out on peak output and a loss in yield.

Why is 1% not possible? Is it solely down to cable cost? If you explain this to your client then they may be prepared to replace it.
 
I think both Markc and Ramjam have valid points ,I can't see a problem with siting the Meter next to inverter ,the Dno might as they'll be the ones losing out but they'll have a few quid to spare from surveys/witness tests etc

the only real issue is the added cost of a correctly sized cable on your quote versus the lads fitting from boxes who know little/ nothing about the design issues ,and with luck they'll be found out quite quickly.

hopefully with systems costing what they do and a more discerning customer base this will happen it would be sad to see it go the way of double glazing and the like.

anyway when we're faced with a large cable run we explain the reasons why and let them make their own mind up ie do they use somone who knows
and explains issues or someone who does'nt mention it .

personally we aim for the 1% Vd recommendation and I would price for another cable as with existing loading plus pv system I would'nt be happy with the csa but thats for the installer to decide
 
I think that's the only honest answer, offer to put the meter co-located with the inverter to ensure that everything generated is recorded then explain that the cable run is less than optimal and offer a price to replace. Some customers want everything right, others wont care as long as it's safe and it pays. Note it in the comments box on the install certificate and move on that way nobody can accuse you of having cut corners or just not having understood what you were doing?
 

Reply to AC cable run 100m info on voltage drop in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top