GaryM

I've seen mentioned on this forum AC isolators modified for use as DC isolators.
I reckon that's exactly what I have, even the lid complete with rotary isolator is interchangeable!
The only difference I can see, apart from the different coloured rotary switchers is the AC is a 3 pole unit and DC a 4 pole using 2 poles in series for both positive and negative.

Is this common practice, even down to the lids being interchangeable?

AC Isolator

ac_1.jpg


ac_2.jpg


ac_3.jpg


ac_4.jpg


DC Isolator

dc_1.jpg


dc_2.jpg


dc_3.jpg


dc_4.jpg
 
Standard practice for Kraus & Naimer and, despite protestations from those with vested interests in other manufacturers' equipment, I am yet to see evidence of it being a problem, providing the isolators are suitabley rated for the jobs in hand.
 
Well the 'DC' isolator is rated at 25A, no problem there and 600 VAC.
I have a single string of 16 modules, each with a Voc of 37.82 VDC, totalling 605.12 VDC at STC.

I guess the only way to know would be to ask the manufacturer of the isolators voltage rating with DC.
 
It is still a modified AC isolator and although they say it is up for the job the internal contacts will have to be switched very fast to stop failure, the question is would you or have you installed one in your house with your wife and kids, this may sound dramatic and over the top but I will never promote or condone the use of a modified AC switch.

It is more than the little daisy chain wire, the contact mechanism also needs changing in its entirity, It goes to show that it is more costly to produce a true DC switch than to modify an existing switch, surely if all the components were right for the job this would not make economic sense. Take a switch and manually add more parts to it ?? two production processes ? Keeps people in work I suppose.
 
Not being an expert in isolator design, I tend to rely on what a manufacturer tells me. If they have tested these isolators to a suitable standard then I have no qualms in fitting them. Like I say, show me evidence that it's a problem and I will reconsider.
 
I will take a picture of a true DC isolator on wednesday when I am back in work you will see the difference straight away, unless someone else here beats me to it, A true DC isolator is wire in diagnal
 
This is an answer to post #6

Install one on a test bed and switch it about 100 times and see if A) it is still working b) there is lots of residue / corrosion on the contacts, 100 times probably overkill
 
Last edited by a moderator:
This is an answer to post #6

Install one on a test bed and switch it about 100 times and see if A) it is still working b) there is lots of residue / corrosion on the contacts, 100 times probably overkill
at what ampage and voltage?

we'd only install the 16amp version for a single string, so max ampage would be around 8-8.5amps, usually at well below 450V. I'd strongly suspect that if you ran that on a test bed it'd last several hundred uses, particularly if you then made allowances for it mostly not being used at full capacity, which in my book makes it fit for purpose given that it's average usage will be around 15-20 times in it's lifetime, and maximum probably around 50.

I'd agree that it's probably best to give them a fair degree of leeway and not push them to their limits, but beyond that I personally think there's some scaremongering going on about this issue, though I do think it's worth everyone just reviewing their specification processes and installer training in light of the recent fire to be sure the DC isolators are being specced and installed to allow for the potential voltages and ampages they could be exposed to, with good margins of error.
 
Last edited:
Gavin

we seem to be butting heads on every topic, if you are happy with it then so be it, but since a true DC isolator is a small cost to the overall isn't it best to be safe than sorry, I have not mentioned the fire deliberately (ok I have now), I just do not like the word modified nor would I invest in something that is modified, not even a car, obviously a car has massive insurance implications.

I am not trying to force people down a route but I do really want to know how many of the electricians in this forum have a modified AC in their home ?
 
Last edited by a moderator:
I have a modified AC in my home.

Like others have said, I don't really see a problem with it. However, I'm no expert on isolators and I go with what a manufacturer tells me.

I very much doubt that the cause of the fire will have been the use of a modified AC isolator - especially considering that the isolator is very unlikely to have been operated since it's installation.
 
GaryM, looking at the picture, which you've provided of the wired DC isolator, I'm afraid it may to be wired incorrectly.

If you refer to the K&N wiring instructions, for DC use, you should use two pairs of links to bridge the contacts - the K&N instructions aren't as clear as they might be in this area and K&N only provide one pair with the isolator. As follows:

Link one between L1 and L2.
Link two between L3 and N.
Link three between T1 and T2.
Link four between T3 and N.
+ supply from PV panels goes to L1.
- supply from panels goes to T3.
+ output to inverter goes to T1.
- output to inverter goes to T3.

This arrangement doubles the contact surface area in use and, in doing so, halves the current passing through the contacts, therefore, reducing the effects of arcing.

Hope that helps.
Roger

....Hmm, actually, this has now caused me to relook at my own interperitation of the drawing....and in doing so, it's not very clear which approach K&N is recommending. In my own mind, paralleling the contacts to double the contact surface area, seems to make more sense than putting two in series, however, the drawing is open to interpretation!
 
Last edited:
We always add 15% to Voc values, and 25% to Isc values of a string when calculating the required ratings of a DC disconector for our clients, if such support is needed. This subject has been batted back and forth many times, the fact is that simply achieving the DC21B ratings is not enough to provide a product that reliably operates time and again with zero deterioration of the contact surfaces. Adequate current/voltage ratings is not only what makes a switch a DC disconnector. Think about why an AC isolator is typically wired straight-through (terminal arrangement) and DC switches aren't. Think about why arc-cooling chambers are built-in to IMO/Santon switches but don't existing on most ABB and K&N modified AC units. Think about why contact surfaces are self-cleaning, knife-edge arrangements in a DC disconnector, rather than separating in a 180degree plane as per most AC switches.

Personally, I believe the reason for the historical and habitual use of inadequately designed "DC switches" (which more often than not are modified AC isolators) is that there has been a significant lack of understanding in the marketplace when it comes to switching DC and some manufacturers have simply pulled the wool over some people's eyes. Some brands have had a significant share of the market because of this, NOT necesarily because of the commercial difference between an AC isolator and a DC disconnector. When looking at the overall cost of a system, £10 or £20 more spent for a true DC disconnector should not compromise the competitiveness of the end-customer's pricing. In fact, using "built for purpose" equipment should be a selling point from the designers/installers point of view! I always advise people not to compare "apples with pears" when purely looking at the commercial differences.

There was a chap on here recently who worked for K&N Tech dept who, when asked about the small print "DC21B when switched with rapid handle operation" on their spec sheets said that it was perhaps removed from their documentation now and that it was not really relevent anyway. In my opinion, it is extremely relevent and was somewhat glossed over for a very specific reason.

There's plenty of info on this subject available, both on here in previous threads and on various websites including our own. Yes, I am biased as we sell IMO and Santon switches. However, the reason we only promote those brands is due to the considerable time I spent a couple of years back investigating the nature of the design of "other" units and their short-falls in performance and reliability. So, biased yes, but only from a technical point of view!
 
GaryM, looking at the picture, which you've provided of the wired DC isolator, I'm afraid it may to be wired incorrectly.
it's not.

well, we generally wire the panels into T1 & T3 rather than T2 & T4, but am pretty sure that's just our convention rather than serving any practical purpose.
 

Reply to AC / DC isolators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock