It has been a long time since I installed an inverter in a loft. I'm doing one tomorrow and I can't recall whether an AC isolator would be required at the CU. Obviously it would be at the inverter but I seem to recall the rules being relaxed for the isolator at the CU?
 
Have a look at 2.3.3 in the guide. It needs careful reading even though apparently simple. I am sure many would argue it is good practice that the 'main ac isolator' is NOT in the loft as that might not be considered 'accessible'. However, if you have a DP mcb or rcd in the CU dedicated to the PV then either could fulfill the 7671 and Guide requirements for an isolator.

Normally when I have done a loft I have done x2 isolators, one at inverter and one by CU, but where inverter is in garage or utility room and isolator is easily accessible then no need for another by the CU.
 
Thanks Bruce.

To be honest, I didn't think 2.3.3 was that clear to be honest.

It is a tough one as the CU is in a converted garage - it is now a kitchen - and AC isolators are pretty ugly things.
As you say, a DP breaker should satisfy the guide requirements.
 
As you say, a DP breaker should satisfy the guide requirements.
hmm, that's odd, I'd not noticed that revision from the draft, and had been assuming the wording from the draft had made it into the final version.

here's the draft version
An accessible means of isolation shall be provided to isolate the a.c. circuit. MCB’s, RCD’s and main switches installed in accordance with BS7671 and in an accessible location can be used to fulfil the requirements for an accessible means of isolation.
I also can't understand why it now has a paragraph instead banging on about unswitched fused connection units being acceptable. Seems very odd.

We've used dual pole MCB or RCD for the isolation point near the consumer unit / incoming supply connnection on virtually every install we've ever done without any problems. At the end of the day, it is complaint to BS7671 for the method of isolating a circuit, otherwise all other circuits would similarly need to have their own rotary isolators next to the CU.
 
I also can't understand why it now has a paragraph instead banging on about unswitched fused connection units being acceptable. Seems very odd.

Yeah, that part is bizarre.

We've used dual pole MCB or RCD for the isolation point near the consumer unit / incoming supply connnection on virtually every install we've ever done without any problems. At the end of the day, it is complaint to BS7671 for the method of isolating a circuit, otherwise all other circuits would similarly need to have their own rotary isolators next to the CU.

This is exactly how I see it. If it is to comply with 7671 then it is no issue - but is it there for DNO use?
 
Yeah, that part is bizarre.



This is exactly how I see it. If it is to comply with 7671 then it is no issue - but is it there for DNO use?
if it were then it would need to be in the meter cupboard, otherwise if they need to access the property anyway then they should be able to use an MCB same as the rest of us.
 

Reply to AC isolators - still required at CU? in the Green Lounge (Access Only) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Thank you! I will add a manual transfer switch. I was hoping that I'd be wrong and it wouldn't be an issue. Sigh. I guess I'll dig out the...
Replies
4
Views
225
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
261

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top