Given the advancement in technology and the high amount of potential DC in electrical systems. An AC RCD that won’t work, invokes so many further regulations for circuits that need RCD protection that no longer do! 100% C2 in my opinion
You might be able to make such a case for specific installations, but as a blanket statement I'd imagine it would be dificult to back up.
How would you justify coding every Type AC RCD as "Potentially dangerou’. Urgent
remedial action required"
What potential danger exists in the average home with Type AC protection?
The AC RCD is essentially rendered useless due to DC current. So off the top of my head circuits within a bathroom, sockets supplying external equipment, electric showers, cables in walls less than 50mm from the surface…all require RCD protection in a standard home, however if the RCD doesn’t work, how is that not potentially dangerous? I wouldn’t like to be the one justifying my case to the man in the wig over this one!
Can you clarify if you mean an RCD that won't work as it has failed or an RCD that won't work due to DC current injected by a downstream appliance?
I may have grasped the wrong end of this particular stick, but in my defence your OP is open to misinterpretation and thread title suggests blanket C2 for Type AC protection.
An RCD that won’t work due to DC current injected downstream! Apologies, I wouldn’t say a blanket C2 but certainly more common than not in my opinion
If you read the Best Practice guide #4 for EICR coding (Nov 2022) from Electrical Safety FIrst, it states for "A Type AC RCD installed where a Type A RCD required" to be coded as C3.
OP has clarified they're referring to an RCD that fails to operate.
It also says that coding is entirely at the discretion of the inspector and the document is merely a guide. I would rather be fussy and improve a system than be lazy and have someone’s death on my conscience. Honest question, if you know an AC rcd may not work in a fault situation, explain why you would code it as a C3 and negate the need for someone to fix it. Imagine a child sticks their finger in a lamp holder? But the rcd fails…
A short while back we established that you were commenting on failed units, but now the conversation seems to have shifted to RCDs that 'may not work in a fault situation'.
How are you establishing that an RCD may fail to operate?
As for coding being at the discretion of the inspector, that's the sort of argument applied by testers who blanket code insulated CUs as C2.
Coding should be back up by regulations and sound engineering judgement. It should not be whimsical in nature.
It’s common knowledge that DC current in a circuit with an AC RCD impairs it’s ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!
Yet for most of those 20 years you were completely unaware of the issue, until Youtube broadened your knowledge?
I was hoping for an explanation of your testing process, rather than coding on the basis of assumption and that's the problem I have with this sort of blanket coding. 'Potential' exists for failure of Type A RCDs. Where they are used for fault protection, do you mandate that additional protection be provided on the basis of 'what if'?
While I don't disagree with the basic premise that Type A protection would be preferable, I do disagee with the idea of coding on the basis of assumption where no potential danger can be demonstrated in a particular installation.
A failed RCD needs to be replaced, regardless of whether that failed unit is Type AC, A or other. A working RCD does not need to be replaced, unless evidence exists to suggest that it will fail to operate (whether that be for the reasons you outline or for any other reason). The average house does not have an induction hob or EVCP and basic LED lamps aren't likely to introduce sufficient DC current to prevent operation of a Type AC RCD. In short, while it may be the case that Type AC protection isn't suitable for a modern installation, most homes do not possess what might be considered a 'modern installation'. Coding should be appropriate to each installation inspected.
I'd like to qualify my previous comments as the OP probably knows nothing about me and might consider them to be argumentative or harsh. The comments weren't intended to be either, but as an apprentice I find myself disappointed and frustrated when no logic is apparent behind blanket statements.
We're all entitled to our opinions, but equally we should be able to substantiate them as bold opinions are likely to be challenged.
Tl;dr... No offense intended, but I want to learn and want to do so in an informed manner.
If the RCD is there for additional protection then it is possible that it should be a C3 as it is additional protection and not the primary protection which is potentially compromised.
If there is a definate, confirmed presence of DC leakage currents which will alter the operation of a type AC RCD then that is a different story to guessing that there maybe might be an issue.
An RCD is unlikely to assist in that situation anyway. If a child sticks their finger in a lampholder then they are more likely to make contact with both the live and neutral, this will result in current flowing through their finger which the RCD will see as normal load current.
Indeed they do, but I must admit I find this suggestion somewhat questionable. Surely if an RCD is required, and the circumstances of the installation dictate that it needs to be a minimum of a Type A RCD because a Type AC RCD could be disabled by circulating DC currents then a C3 Observation seems overly lenient. But alas, you are correct that this is what that Best Practice Guide suggests.
Common knowledge indeed, but one thing that remains mostly unanswered is how the DC current comes to be passing through the RCD in the first place? Presumably a circuit must be completed for it to flow, so is it deliberate, or is it due to faulty equipment? And what route does it take? Any answers (with sources) appreciated
Another reg that I think is daft and has been changed for changes sake. I would have thought that in 99% of situations an AC RCD will be just fine, certainly in all the EICR's that I've done over the last few years and all the installations that I've done with AC ones they all tripped off no problem under test, the ones that didn't were physically faulty (BG ones for eg) despite houses being full of LED lamps, TV's, phone chargers, HOB's, washing machines etc etc.
My house is a perfect example, I have lots of electonic goods, your typical house, probably more so with my computer stuff, yet the 10 year old RCD trips off every time the oven is on for more than 30 minutes, its needs a new element.
From what certain people are saying I have a C2 problem in my consumer unit which is potentially dangerous, no RCD at all would be a C2 as well, so going by that logic I might as well ditch the RCD altogether and be no less safe than I was before, then I could have a roast dinner and not just a pizza.
It has been changed because the older RCD technology is no longer appropriate in a modern installation.
Tripping under test conditions is different to tripping under real world conditions.
I think you've misunderstood some basics here.
The RCD tripping due to a faulty oven element does not prove whether or not it has been affected by any DC leakage.
DC leakage occurs from electronic loads, especially switch mode power supplies and the like.
Lucien wrote a pretty good explanation of the DC leakage subject relatively recently. It should be possible to find it with a search.
Well if it has been affected by DC leakage then it still tripped so all is good and if it hasn't been affected by DC leakage then all is good too. My house has all the possible scenarios that could cause DC leakage but the RCD still trips merrily away.
It’s common knowledge that DC current in a circuit with an AC RCD impairs its ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!
Sorry on behalf of everyone else we didn’t realise you had a degree, I’ll be the first to bow down to you. Our years practical experience working on site years means nothing when the piece of paper enters the room.
I think there are valid points on both sides of this debate.
In general if an RCBO seems to work (and I usually try a type A test too even though it isn't required) then I feel I have no evidence that it isn't doing it's job, and it's a C3.
In practise I find most Type AC RCBO's will trip if tested on a Type A setting, and normally within required times. (Using the x5 test they sometimes didn't quite make 40ms but only by a few ms.). So far the only ones that didn't trip also didn't trip on a type AC test because they were stuck or broken.
If you remember the older No Trip loop testers used to used DLOK and deliberately inject DC to blind the RCD, and it's telling that this technology had to be abandoned as it fails to work on almost all RCBOs.
In general I'm more concerned about older shared RCD's where the cumulative DC leakage from multiple circuits can be higher, and the older ones seem to be more susceptible to DC blinding in the first place (backed up by the fact that older loop testers could successfully 'fool' them).
I'd love to get a DC leakage clamp meter to help make better informed decisions but it hasn't made it to the top of the wish list yet.
Just because it trips it doesn't mean it is tripping at the right current or within the right time period.
This isn't a binary process whereby the RCD either is or is not prevented from working at all.
I'm wondering if this entire thread has missed the point. The OP seemed to be proposing a blanket C2 for any type AC RCD circuit, then did a bit of a back-track.
This is what really boils my P about 'inspectors' who lack the fundamental knowledge and learning to apply some engineering principles and instead just go looking for any reason to find a higher code because they think it justifies their existence.
Absolutely, there are instances where potentially use of an AC type rather than an A, B or F might be innapropriate due to bias and blinding, that's a part of mine, Davesparks and several others on here's specialism(s) every day, but it bears no relation to a lighting radial of 60W BC's in Mrs Miggins pie shop where an AC type is still perfectly acceptable as it provides entirely appropriate protection against the risk.
Sure, the lines have become murky in domesttic installations due to the changes in household and consumer appliances but if you are going to be ballsy enough to make an assertion about risk, then at least understand that risk and be able to justify it. If you think that a circuit might be compromised then simples - test it. Apply a ramp test when it's in normal use and see what happens - if your assertion that it needs a C2 due to DC blinding is true then it won't trip on a standard ramp test. If (when) it does, then you'll know to stop talking ball hooks and give it an entirely appropriate C3.
With regard to code for AC RCD's. If it is tested with all loads connected and passes then I will C3 it, if it fails then C2 for obvious reasons.
In my working life as an electrician I can honestly say that apart from the obvious failures of RCD's I have only ever tested 3 that have been blinded by DC they were all within the last 2 years and all of them were the older BS4293 type of RCD!
It's funny as I have been having issues at a unit I have been testing with Welding plant melting the earth conductor insulation the entire length of a circuit.
That circuit is protected by an MEM 4pole 63a 30ma RCCB and a 32a MCB. The circuit has never tripped out until recently.
Upon inspection of the welders there doesn't seem to be any internal link between the main earth and the Welding plants return earth which was excellent but didn't solve my problem. I then clamped the circuit CPC and the supply cable to see if there was any leakage, there was no AC leakage.
I forgot the DC clamp meter so am going back tomorrow with it to see if it is DC that is blinding the RCD and helping to melt the earth conductors insulation!
Sy
I've not yet had an issue with them not tripping but I don't think it's possible to fully simulate the worst possible case either. I've never turn on someones inverter driven washing machine, rapid boiled some water on the induction hob, with the fridge left open and fired up the PC to see if it would still trip with everything going full pelt. Usually, I warn them that the power will go off so everything minus the fridge is off in fact.
I think Dave's point about RCDs being additional protection in many situations is very poignant too.
If appliance manufacturers could give more useful information regarding DC leakages we could make a much more informed decisions and the manufacturers could tell customers that their new hob will lead to firey death if that is true so we don't have to be the doomsayers.
I expect very few items actually leak DC under normal conditions, otherwise they will fail the PAT style of test on insulation. They might inject DC components under fault conditions, but that is another matter.
My own understanding is C2 codes are for situations that are a single fault away from danger (C1 is immediate danger, C3 is not to current specifications but needs an unfortunate combination of circumstances) and as such for most cases type AC RCD are not that.
If they are on an EV or PV system then yes, a single fault could be a DC fault and then "say your prayers Blackadder, its poker time!"
Edit: Fun fact, the actor who played the baby-eating bishop of Bath & Wells in Blackadder S2 'Money' was Ronald Lacey, who also played the Gestapo officer in the Raider of the Lost Ark.
N.ireland
United Kingdom
Heavily Qualified Electrician / Teacher / Tutor - etc
AC RCD’s C2? Absolutely!
UK
Thread Tags
J Sparks,
pc1966,