View the thread, titled "ac supply" which is posted in Solar PV Forum | Solar Panels Forum on Electricians Forums.

G

gordysolar

Is it best to connect ac supply from origin or is it ok to connect to a sub board in a garage? if not get cable back to house board where meter is?
 
Last edited by a moderator:
Is it best to connect ac supply from origin or is it ok to connect to a sub board in a garage? if not get cable back to house board where meter is?

I dont see why you couldn't use a sub board, as long a the VD & cable supply ok
 
I dont see why you couldn't use a sub board, as long a the VD & cable supply ok

No problem at all but supplied from source via a henley block would allow the customer to measure generated current and usage current independently of each other, if that's what they would prefer to do.

Mine is supplied from a spare way in my main consumer unit as I'm fine with the way I monitor energy.
 
yeah henley block and 10mm tails into a 2 way db and a 16 amp mcb i always put


And if i am reading the original post correctly he is asking if he cant get a cable back to the origin so a henley block/tails/CCU scenario isnt a viable option.

And always a 16a mcb? No RCD/rcbo protection ever? Surely not always mcb's unless every instal is the same?

You could possibly use the existing db in the garage if-

1. The supply cable is of sufficient size to allow for 1% volt drop.
2. Depending on the inverter you are installing, the db will almost certainly have rcd protection at either origin or at db so it could be problematic to instal a 16a mcb/rcbo to this db.
3. Err
4. :D
 
Last edited by a moderator:
OSG 2.2.3
Taken from the OSG.... Page 17

2.2.3 Meter Tails
These are part of the consumers installation. They should be insulated and sheathed or insulated and enclosed in conduit or trunking. They are provided by the installer.

Polarity should be indicated by the colour of the insulation and the minimum cable size should be 25mm. The distributer may specify the maximum length and the minimum cross sectional area.

Where the meter tails are protected against fault current by the distributers cut out the method of installation, maximum length and minimum cross sectional area must comply with the requirments of the distributer.


knew i read it somewhere
 
That's the OSG, a guide only for people who can't engineer solutions for themselves. No problem at all with 10mm tails supplying a one way CU with a 16A MCB for a PV system.
 
Shouldnt the tails be a minimum of 25mm according to the new ammendment?

Not according to my assessor! the maximum current under useage is 16 amps so there is no potential for overload of the 16mm tails. In the event of a fault (i.e. direct short) which is going to fail first, the 1mm or so thick fuse wire or the 16mm tails. IT'll be the fuse every time so 16mm tails are fine on a garage sub board (or even on a domestic board if your maximum demand is less than 80ish amps that I can't recall off the top of my head)
And of course 16mm tails are a whole lot easier to work with!!
Even if demand is above the limit you can still use 16mm tails if you fit a main breaker at the point of origin of a suitable size. This was the scenario I discussed with my assessor where it was impossible to change the meter tails on a board change without doing substantial damage to the property.
 
Last edited by a moderator: