Acceptable spur length from fcu | on ElectriciansForums
Discuss Acceptable spur length from fcu in the Australia area at ElectriciansForums.net
P
Penance
Putting a final ring in kitchen and will have a fcu on the ring for the cooker hood.
I want to then run from fcu up wall to a flex plate.
Due a window above the fcu I can't run straight up and it also wouldn't be where the outlet needs to be. I can run down from the fcu, under the floor and then back up where it is needed. That run would be around 4 meters, is this ok?
I'm sure I read in the regs that it could not be longer than 3 meters but damned if I can find it now.
No, there is no maximum length in the reg's but the On-Site Guide recommends "as a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring"
Your spur will not be unfused anyway.
Telectrix, I could but then isolation would be out of reach.
Iq - so I am ok as it is fused?
Can you point me at the reg, looked again and having a wood and tree moment
Absolutely, of course volt drop and Zs would be limiting factors but in a domestic situation and with RCD protection on at least your addition, you'll be fine!
Reply to Acceptable spur length from fcu in the Australia area at ElectriciansForums.net
Thanks for the advice.
Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...