S

sparke

Hi all , trying to get ready for elecsa assesment. planing to show new cu insall on my own home 17th ed of course. Problem is that TTearthing :eek: put in 1 rod got reading of aprox 230 ohms zs(very rocky stoney ground) on socket outlets so put in anoter linked to the first now geting a reading of 154 ohms .
cant find any clear guide lines in regs as to what is acceptable level seems a bit of a grey area. who knows ????
 
this is how i see it the max permitted is 1666 ohms based on not allowing the voltage to rise above 50v
however no one would leave an electrode this high the old rule of thumb was not more than 200 ohms and now you should be aimimg for 100 ohms or less.
also you need to use your ze reading not the reading at your sockets just test purely beetween live on feed side of main switch/rcd and earth to stake with it removed from cu.
with everything else in the board the reading may come down even more.
hope this makes sense.
 
Hey Sparke.

The max permissable RA (earth electrode resistance) (Ze) fir a TT installation is 1667 ohms.

However it is generally taken that RA should not exceed 200 ohms and there are notes on this in OSG.

This should be measured at the C.U on the supply terminals of the main switch with the main earth disconnected and main switch open, same as you would measure Ze.

As you have a reading of 154 ohms then you are under the max of 200, but as you are in rocky ground this result may be unstable and the ELECSA man may refer to this as it may change significantly and go over the 200 in different weather conditions

To absolutely cover yourself are you able to get a third rod in?? if so it would be worth doing I feel.

Hope this helps.
 
Hey.

Just as a bit more info, I carried out a lot of work for a pipeline construction company during a project they had in my area.

All the construction yards were TT installs and we were achieving RA's of between 4 and 5 ohms, on rocky ground also

This was with 120mm earth and somewhere in the region of 10 14mm copper rods though, in 5 sets of 2.

I know this would be too extreme for you domestic situtation but it just shows that you can achieve a low RA reading in any circumstance.
 
Hi all , trying to get ready for elecsa assesment. planing to show new cu insall on my own home 17th ed of course. Problem is that TTearthing :eek: put in 1 rod got reading of aprox 230 ohms zs(very rocky stoney ground) on socket outlets so put in anoter linked to the first now geting a reading of 154 ohms .
cant find any clear guide lines in regs as to what is acceptable level seems a bit of a grey area. who knows ????

hi there

Is all the ground around you rocky ?

we ran a copper tape to a couple of square grids made out of copper buried at a couple of different depths this gave both an increased contact area with the earth and did not mean having to go deeper with constant rods all the time.

just a suggestion it may help you

we used a couple of bags of a powder which you wet once you put it in to give a better / lower resistance cannot think of the name but it sticks like **** to a blanket lol The big boys use it to ground out airfield installtions etc.


cheers
 
Last edited by a moderator:

Reply to acceptable zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top