i know some, probably tel will make a joke about this, ..i can see it coming so i'l get in first :this isnt about bad value day outs sorry tel
So ive read many posts on this subject and opinion seems divided.
On testing a MEM 100he mains switch rcd with all breakers off,link from the main switch to neutral bar disconnected(croc clamped meter ends to neutral at switch and line on the main bus bar and lastly clamped third lead to earth bar in comsumer unit). energized switch with ramp test selected on meter,selected test ..the rcd tripped at 23 mA.Cant find any technical data about this device to i woundered what thoughts are about this.This board has given random nuisance tripping for a very long time,but with all ccts disconnected i thought ide get a higher reading of maybe 28 mA ..Any advice much appreciated
So ive read many posts on this subject and opinion seems divided.
On testing a MEM 100he mains switch rcd with all breakers off,link from the main switch to neutral bar disconnected(croc clamped meter ends to neutral at switch and line on the main bus bar and lastly clamped third lead to earth bar in comsumer unit). energized switch with ramp test selected on meter,selected test ..the rcd tripped at 23 mA.Cant find any technical data about this device to i woundered what thoughts are about this.This board has given random nuisance tripping for a very long time,but with all ccts disconnected i thought ide get a higher reading of maybe 28 mA ..Any advice much appreciated