I have been asked by a client to add a heat detector point into a gymnasium which at present only has break glass points.

Can I run a 4 core cable (MICC) from the break glass point, which has two MICCs at present, and connect the cables appropriately in the break glass point?
 
Done similar plenty of times with my old firm so i'm guessing it's okay however someone with a better knowledge of BS5839 Pt.1 would be able to advise you further.
 
you need to maintain a radial with no spurs. easiest way is a 2 core from the end of line and relocate the eol device. alternatively, break into the circuit with a galv tee box and use a 4core , 2 cores to new detector and 2 cores back, jointing in box to preserve the radial.
 
just as telectrix says is fine thats how we did it when altering and installing fire alarms the only thing i would add is that the cable you add on should be of the same fire rating or above of the one you are adding too
or at least that is what my old boss always said
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adding fire point
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
brizospark,
Last reply from
littleeley,
Replies
3
Views
931

Advert

Back
Top