B

brizospark

I have been asked by a client to add a heat detector point into a gymnasium which at present only has break glass points.

Can I run a 4 core cable (MICC) from the break glass point, which has two MICCs at present, and connect the cables appropriately in the break glass point?
 
Done similar plenty of times with my old firm so i'm guessing it's okay however someone with a better knowledge of BS5839 Pt.1 would be able to advise you further.
 
you need to maintain a radial with no spurs. easiest way is a 2 core from the end of line and relocate the eol device. alternatively, break into the circuit with a galv tee box and use a 4core , 2 cores to new detector and 2 cores back, jointing in box to preserve the radial.
 
just as telectrix says is fine thats how we did it when altering and installing fire alarms the only thing i would add is that the cable you add on should be of the same fire rating or above of the one you are adding too
or at least that is what my old boss always said
 

Reply to Adding fire point in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
246
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
2
Replies
13
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
2
Replies
10
Views
1K
I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top