Hi guys,can you add a n extra sockets to a sockets if there is no rcd protection.
Thanks in advance for answers.
Rcd spurs are not recognised by BS7671 as a means of providing additional 30ma rcd protection so it would have to be listed as a departure.
... that's still OK though isn't it? As you say, if it's listed as a departure. As long as the cable installation method does not require RCD protection presumably? Does an RCD spur protect the load side or supply?
Your departure would have to have the same level or better than suggested by BS7671, not something I would be trying to prove.
I'm sure I read an article somewhere where at least one of the schemes decided that it was an oversight when writing the list of devices and that all things considered they were acceptable.
However I'm not sure ' I think I read it on the internet somewhere.' would be a valid defence. :D
Read and understand APPN15 EVEN THE VAULTED SCHEMES have to apply 7671 to their acceptance procedure. Apart from the obligatory numerous pound notes, and hoops you have to jump through you need to join every 12 months, just to keep parasites in beer money. Going to get deleted isn't it?
Appendix 15 makes no reference to additional rcd protection so maybe you should read it.
Reply to Adding socket in the UK Electrical Forum area at ElectriciansForums.net
Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic
In the picture of the socket, it looks like one of the neutrals may have been screwed in over the insulation. Therefore, the live may also have...