B

Blacktail

Feeding two outbuildings by overhead cable from TNCSsupply. Building one, steel framed barn,earth floor etc. Building two, stableblock, concrete floor/block walls and steel roof frames. Approx 20 and 30m respectively from supply.

For all obvious reasons going to TT each building and fiteach with its own DB. Sub main will run fromsupply to outside of first building to junction box. Here it will split to feed DB-1 and feed, via overhead, to stable block and DB-2.

Do i need to consider the “ daisy chained ” feed from buildingone to building two, to now be a TTsupply and therefore require additional protection. It won’t be supplied from DB-1 as it willsplit at the junction box.

Armour/cpc continuity will be maintained through junctionbox to downstream of DB-2. Bounced thisof my “Approver” and they say second feed requires additional protection as itis now TT. Not sure.:crazy:

 
Use a 300mA S type RCD for outbuildings submain supply, that should cover you for the additional protection. I wouldn't be tempted to install a standard 300mA RCD, as you will stand a pretty high risk of not achieving discrimination with the downstream 30mA RCD devices within the two outbuildings....
 
As Eng said, you need the 300mA RCD as it's an agricultural premises, but for discrimination purposes make it an s-type. One thing I will add though is that the second feed in the case of the installation you are describing in no different to the first feed. It requires no more protection that the first either as they are both one and the same daisy chained or not. Also, whoever told you it needed additional protection is wrong, additional protection can only be provided by a 30mA RCD or supplementary bonding.
 
Each building should be it's own TT system, maintain the supply earthing for the submains and divorce each building separately to it's own TT earth.
I suppose you could have a long earth conductor from a rod at building 1 running to building 2 and use a single earth point, but this would not be good practice.
 
Think i must of misread that the original supply was PME, I was taking it as all being TT!!
So as R Burns states, maintain the TNC-S earthing for the submain supply and divorce at each of the two buildings in favour of a TT system(s)

There is however no need to keep the two buildings TT systems separate. Each building should have it's own earth electrode postion(s) but there is nothing stopping you from linking those positions. In fact, it will probably be advantageous and resulting in a much improved overall lower Ra value to do so.
 
Thanks all. Seem to be having a lot of problem posting reply, also sorry for all the typo's. Had to cut and paste to get anything in the dialogue box and transposed v.badly. So as I was thinking really.

"The Approver"? The NICEIC helpline of course. I actually contacted them to confirm if Ex dairy farm, redundant farm building and a goat in the horse house falls under 705.

Thanks again
 

Reply to Additinal protection to TT submain in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
Leaves the potential nuisance of knocking off a raft of equipment unnecessarily
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top