Hi, if im adding to a ring main circuit on a minor works cert do i have to change the bs3036 fuse to a rcd protection. Adding to the ring main entails coming off back of excisting socket creating a spur having cable through wall less than 50mm deep.


Can you please advise
 
522.6.6 - Cables Installed in a Wall or Partition. This says that: 'A cable installed in a wall or partition at a depth of less than 50mm from the surface of the wall or partition shall':
Incorporate an earthed metallic covering which complies with the requirements for a protective conductor of the circuit concerned, the cable complying with BS 5467, BS 6346, BS 6724, BS 7846, BS EN 60702-1 or BS 8436, or;
  • be enclosed in earthed conduit, or;
  • be enclosed in earthed trunking or ducting, or;
  • be mechanically protected against damage, sufficient to prevent penetration of the cable by nails, screws and the like, or;
  • be installed in the traditional 'safe zones' - 150mm from the top of the wall or partition or within 150mm of an angle formed by two adjoining walls/partitions, and horizontally or vertically to any point, accessory and switchgear.
 
522.6.6 - Cables Installed in a Wall or Partition. This says that: 'A cable installed in a wall or partition at a depth of less than 50mm from the surface of the wall or partition shall':
Incorporate an earthed metallic covering which complies with the requirements for a protective conductor of the circuit concerned, the cable complying with BS 5467, BS 6346, BS 6724, BS 7846, BS EN 60702-1 or BS 8436, or;
  • be enclosed in earthed conduit, or;
  • be enclosed in earthed trunking or ducting, or;
  • be mechanically protected against damage, sufficient to prevent penetration of the cable by nails, screws and the like, or;
  • be installed in the traditional 'safe zones' - 150mm from the top of the wall or partition or within 150mm of an angle formed by two adjoining walls/partitions, and horizontally or vertically to any point, accessory and switchgear.


Hi ive just read this on the Electrical safety council website, i know what your saying but what interpretaion do you get from this :
Q4. A switched, fused 13 A connection unit is to be added to an existing circuit. The work is not being carried out in a special location and the existing circuit has no RCD protection. The incoming services are bonded and the new switched fused connection unit is to be flush mounted 150 mm horizontally from an existing socket, and connected with wiring concealed in the wall. What is the reasonably expected for the installer to do to comply with the 17th Edition?
The connection unit does not require additional protection by RCD, though at least the extended part of the existing circuit will need to be suitably protected (by RCD or other means).

Regulation number(s)
  • 522.6.101 to 522.6.103
 
The SFCU is for a specific piece of equipment, st that's why IT doesn't need RCD protection.

BUT the new bit of cable is buried in the wall. So THE CABLE must be RCD protected. Which inherently makes the SFCU RCD protected!

You could change the existing socket to an RCD fused conn unit, then put a socket adjacent if you still need one there, and connect your new addition to the RCD fused conn unit.
Maybe if the existing socket is a double, change to a DUAL back box...

There's always a way!

Simon.
 

Reply to Addition to ring main circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top