D

daver

Am just about to start a job on 3 story house which will become 8 individual flats.
Am running 16mm T&E from incomer to each DB. I was going to add an additional 10mm CPC to each flat but have had conflicting advise on this.

Some say do, some say no need.

Is there a definative answer.

Cheers

Dave
 
MP. Just had a look at this and it is as I said in my PM to you. Using SWA, all cores are same size plus you have the armour.
T&E easier to use, but with 16mm you only have a 10mm CPC.
According to table 54.7, Line conductor S =< 16mm should use a cpc of equal size.
So running a 6mm with it brings it up to 16 mm and meet regs.

We found it ourselves

Thanks Guys
 

Reply to Additional CPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about...
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top