Jeffmo65
Hi Guys ?
We have been asked to install some additional bits of kit to a small supermarket . Everything is metered ie; lighting , general power refrigeration and so on . We have been told by the consultant that they have an ASC of 60 KVA . I visited site the other day to carry out some investigation . On clamping the singles , I found that
L1 = 128amp
L2 = 92 amp
L3 = 112 amp
Fitted are 200 amp fused main switch .
Now they are also saying they are max ASC Of 57.5 KVA according to their metering analysis .
Doing some 3 phase maths , their statement that they are 2.5 % under agreed ASC doesn't run true as I have them over already . Any thoughts chaps
We have been asked to install some additional bits of kit to a small supermarket . Everything is metered ie; lighting , general power refrigeration and so on . We have been told by the consultant that they have an ASC of 60 KVA . I visited site the other day to carry out some investigation . On clamping the singles , I found that