Hello,

I have a 6-way Hager consumer unit with a 100A 30mA rcd main switch, circuits are on individual mcbs. It is in a commercial environment.

If i wanted to add an extra socket into the rfc would the fact that there is a 30mA rcd main switch satisfy the requirement for additional protection for socket circuits?

Could it then be stated on a minor works certificate that there is a departure from bs7671 as circuits are not divided to avoid hazards and minimize inconvenience in the event of a fault.

Any help on this would be much appreciated!

Thanks
 
Hello,

I have a 6-way Hager consumer unit with a 100A 30mA rcd main switch, circuits are on individual mcbs. It is in a commercial environment.

If i wanted to add an extra socket into the rfc would the fact that there is a 30mA rcd main switch satisfy the requirement for additional protection for socket circuits? Yes.

Could it then be stated on a minor works certificate that there is a departure from bs7671 as circuits are not divided to avoid hazards and minimize inconvenience in the event of a fault. Yes.

Any help on this would be much appreciated!

Thanks

As you say not an ideal situation with all circuits being on the one RCD but difficult to argue with a customer the fact.
 

Reply to additional protection in the Australia area at ElectriciansForums.net

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
884
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top