Hi
I have been asked to put in another socket in a kitchen for a washing machine. Now we are taking 1m of 2.5 clipped in a cupboard however the property does not have any RCD protection. The board is old with them plug in MCB's. Now for reasons to complicated to detail I have no room to install a RCB to protect the whole house and the customer does not want a new Distribution board.
Now according to the regs any additional to a ring main must have RCD protection so I was at the point of saying sorry just cant do it however, on close inspection I noted 411.3.3. Does this mean if I cut the plug off the washing machine and terminated into a fused spur I could get away with no RCD? It would then be a dedicated point for a fixed appliance and nothing else could be used from this point.
Any thoughts? or do I walk away.
Cheers
I have been asked to put in another socket in a kitchen for a washing machine. Now we are taking 1m of 2.5 clipped in a cupboard however the property does not have any RCD protection. The board is old with them plug in MCB's. Now for reasons to complicated to detail I have no room to install a RCB to protect the whole house and the customer does not want a new Distribution board.
Now according to the regs any additional to a ring main must have RCD protection so I was at the point of saying sorry just cant do it however, on close inspection I noted 411.3.3. Does this mean if I cut the plug off the washing machine and terminated into a fused spur I could get away with no RCD? It would then be a dedicated point for a fixed appliance and nothing else could be used from this point.
Any thoughts? or do I walk away.
Cheers