L

LlandrilloSpark

Fellas is it permissible to run a single 2.5mm in a loft or do really need double insulated?, there has been an attempt to add an earth to the circuit before but they missed the switches out and some fittings are 32Ohm R1+R2, it's in a bungalow so should be easy
 
I think it has to be over 6mm if you're installing it without mechanical protection.
Could you just rip it out and do it all in bog standard T&E? Might be easier, neater, cheaper etc.
 
I had thought of a circuit rewire but only 4 lamps are effected and the switch back boxes have plastic lugs so they don't even technically need earthing if the patress screw doesn't touch the back box, and all the switched are PVC, cheers for the 6mm advice
 
It has to be 4mm min if it hasn't got mechanical protection (543.1.1) but what's usually the hardest part adding one is that it has to be incorporated in the same wiring system or in the immediate proximity of the live conductors (543.6.1) which means dropping one down to switches etc so it's probably easier to just rewire.
 
Think even the back boxes have to be earthed even if not technically required now to allow for somebody putting in metal casing switches in the future .
 

Reply to Addng cpc to two core lighting circuit in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top