lionelmcc

Hi chaps,
I visited a house the other day which has a granny flat. this is supplied by a 16mm T&E On a 50A Breaker with 30mA RCD from the CU in the house. There would not appear to be any extra earthing run along with the submain for the granny flat.
would i be right in thinking that the 6mm in the T&E is inadequate for the main earth between the two CUs?
Should I run a 10mm alongside the T&E?
 
The section of the Regs that cover this is 543.1.3, but to use the equation you need to know more about the installation. The pfc at the sub board is the main controlling factor feed this into the equation and it gives you the cross section of the sub-main. I did a few assumptions and came up with 9.7 sq mm.

Also the rukle of thumb I was taught in class was that the earth should be not less than 1/2 the size of the phase conductor. So again for a 16mm cable the earth should be 10mm.

However, is it a very old cable? most modern cables would comply with these requirements, so I would have thought the earth with a 16mm T&E would already have been a 10mm. Personally I cannot look at a cable and say if it is 6 or 10. (and neither could my inspector!) It may be worth a comparison with a known cable.
 
If you use the adiabatic equation does the fact that an RCD is present come into it?

For instance if the Zs figure was at the maximum allowed for a 50A breaker (0.92) then you would have a fault current of 250A.
If the RCD operates within its maximum allowed time of 40mS then the adiabatic calculation gives a minimum size of 0.5mm :confused:
 
That's a good question. It seems to be an anomoly in the Regs, although they do say that you must not rely on an RCD as the only means of ADS. So I guess the answer is no, you still need the full size of earth.

Has anybody tried the NIC tech line on this one?
 
they do say that you must not rely on an RCD as the only means of ADS. So I guess the answer is no

Hi NoSparks,
That was my thought too but wondered about TT installations.
If you had a Ze of 20 Ohms the PEFC will only be 11.5A, so the only protective device that will operate would be the RCD which makes it the only device that can be used in the equation.

I have not phoned any technical helpline as I am an employee and not a member of a scheme, but certainly curious about this senario.
 
Last edited by a moderator:

Reply to adequate earth? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
827
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top