Good evening everyone,
I'm doing 04A1 practical assessment at the moment, and I'm confused with adiabatic equation. It seems easy when tutor is around, but when you're trying to sort it out on your own, a lot of questions appears) I would really appreciate if you could help me out.
Here is one question, please delete it if it's inappropriate here.
Questions are:
1) If I (earth fault current) is 214.2A do we have to change our Circuit breaker: 6A 60898 Type B (30A) to a breaker that handles 214.2A+ ?
2) Our tutor said that the minimum CPC in singles should be 1.5mm[SUP]2[/SUP] do I have to use that even if 1mm[SUP]2[/SUP] is sufficient?
3) I've read on the forum that:
If you are using the tables in Appendix 3, remember to use the current values in the table, rather than the measured value. So what about graph values?
4) Tutor showed another calculation method without Zs, he toot I=circuit breakers max current(30A for TypeB), and t=max TN-C-S time(because in the assessment it's that) = 5s (or it could be that he took the maximum TypeB time which is 5 as well), and S= (sqrroot 30[SUP]2[/SUP]*5)/115 = 0.5833mm[SUP]2
[/SUP]It seems confusing to me that there are 2 ways of calculating the equation.
Much appreciated.
I'm doing 04A1 practical assessment at the moment, and I'm confused with adiabatic equation. It seems easy when tutor is around, but when you're trying to sort it out on your own, a lot of questions appears) I would really appreciate if you could help me out.
Here is one question, please delete it if it's inappropriate here.
8)The circuit supplying lighting to the W.C, office, etc (Gr4) will be wired in PVC singles in conduit and trunking to reference method B.The circuit length is 20m, and the trunking contains 3 other circuits. Due to the positioning of the conduit under the light panels in the roof the ambient temperature will be taken as 25[SUP]o[/SUP]C.
a)Using BS7671, design the circuit to supply this equipment. Note all tables you reference.
Procedure:
Ib- design current.
WC = 28W, Store(flourescent) =36W, Office(flourescent) = 58W, PIR = 84W
28*1.8 + 36*1.8 + 58 + 84 =257.2W
Ib = Watts / Volts = 257.2W /230V = 1.12A
In- rating of the protection.
In ≥Ib ( Appendix F 433.1.1) ;
Circuit breaker: 6A 60898 Type B breaker.
In = 6A
It- tabulated current-carrying capacity.
Reference method B trunking,singles, L=20m, 4 total circuits (1 + 3), ambient temp = 25oC;
Ca = 1.03 (Table F1, ambient temperature 25[SUP]o[/SUP]C),
Cg = 0.65 (Table F3. 4 circuits,reference method B)
It ≥In/CaCg; It ≥6/1.03x0.65; It ≥8.96A
Cable size:
From Table F4(i)(Reference method B): 1mm2 = 12A.
12A ≥9.23A
So 1mm2 is sufficient for the circuit.
Voltage drop:
Appendix F
voltage drop= ((mV/A/m)xLbxL)/1000
Table F4(ii)Reference method (6) A&B = 38 mV/A/m for 1mm2 cable, hence:
vd=(38*1.12*20)/1000=0.85V and allowed is 3% (6.9V);
b)Select an appropriate minimum sized CPC, and confirm your selection by calculation. Note all table syou reference.
Liveconductors are 1mm2 according to 543.1.1(The cross-sectional area of every protective conductor, other than a protective bonding conductor, shall be: (i) calculated in accordance with Regulation 543.1.3, or (ii) selected accordance with Regulation 543.1.4) in accordance with Regulation 543.1.4 the minimum CPC should be the same as the live conductor = 1mm[SUP]2[/SUP]
But in accordance with Regulation 543.1.3, calculations should be the following:
Check the CPC by using the adiabatic equation:
Table 4.6 of OSG Column 3 for 1mm[SUP]2[/SUP] gives 1mm[SUP]2[/SUP].
Table B7 of OSG for Type B gives 1mm[SUP]2[/SUP] for fault leve <= 3kA
k=115 (Table 54.3)
Zs=Ze+(R1+R2), Ze = 0.35Ω(TN-C-S max), R1+R2 = 36.20mΩ * 20m = 724mΩ = 0.724Ω (Table I1 for mΩ/m)
Zs=0.35 + 0.724 = 1.074Ω
I=Uo/Zs = 230 / 1.074 = 214.2A
t=0.1s (Fig 3A4)
S=(sqrroot I[SUP]2[/SUP]t)/k ; S=(sqrroot 214.2[SUP]2[/SUP]*0.1)/115=0.59mm[SUP]2[/SUP] therefore 1mm[SUP]2[/SUP] is enough.
Questions are:
1) If I (earth fault current) is 214.2A do we have to change our Circuit breaker: 6A 60898 Type B (30A) to a breaker that handles 214.2A+ ?
2) Our tutor said that the minimum CPC in singles should be 1.5mm[SUP]2[/SUP] do I have to use that even if 1mm[SUP]2[/SUP] is sufficient?
3) I've read on the forum that:
If you are using the tables in Appendix 3, remember to use the current values in the table, rather than the measured value. So what about graph values?
4) Tutor showed another calculation method without Zs, he toot I=circuit breakers max current(30A for TypeB), and t=max TN-C-S time(because in the assessment it's that) = 5s (or it could be that he took the maximum TypeB time which is 5 as well), and S= (sqrroot 30[SUP]2[/SUP]*5)/115 = 0.5833mm[SUP]2
[/SUP]It seems confusing to me that there are 2 ways of calculating the equation.
Much appreciated.