I want to calculate a main earthing conductor for a three phase supply using the old adiabatic equation.

I'm struggling to work out what value of I to use. If you use 230V/0.35 (for a TN-C-S) then you get 657 amps.... if it turns out that Ze is lower, the fault current is going to be higher, so what do you do?

And again with time, do you use 0.1 or 0.4?

Any light shed would be greatly appreciated....

Cheers
 
With regard to time i would go with 5s as it is a distribution circuit.

With 3 phase, pscc will be larger than pefc . edit : Think you need measured values or use table 54.7
 
Last edited by a moderator:
With regard to time i would go with 5s as it is a distribution circuit.

With 3 phase, pscc will be larger than pefc . edit : Think you need measured values or use table 54.7

Thanks Pushrod....... wanted to try and calc if it was possible (as a paperwork exercise) so I had it clear in my head rather than use 54.7.....

Q. would a Pscc fault use the earth path / earth conductor? Got in my head that it would follow 'line - neutral' or 'line - line' and then not come into the equation? Your thoughts?
 
Thanks Pushrod....... wanted to try and calc if it was possible (as a paperwork exercise) so I had it clear in my head rather than use 54.7.....

Q. would a Pscc fault use the earth path / earth conductor? Got in my head that it would follow 'line - neutral' or 'line - line' and then not come into the equation? Your thoughts?

Max PSCC would be L-L as then it would be 400V/Zs, whereas a pefc would be L-E so would just be 230 V/Zs :)
 
On a TN-C-S system, the earthing conductor must also meet the requirements of 544.1.1 and so must be selected from 54.8 rather than calculated.
 
Yes but on a TN-C-S system, the earthing conductor must also meet the requirements of a main protective bonding conductor.
 
Check out 542.3.1

To my mind that is "543 and 544.1.1" so it is just imposing a minimum size of 10mm²; as 54.7 doesn't specify a min size. It just says S = protective conductor if below 16mm². Table 54.7 is a more stringent requirement (ie requiring a larger size) on earth size than 54.8 would be. So IMO i would still in a real life situation size by 54.7 :)
 

Reply to Adiabatic equation calc in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top