Hi guys,

I had a brain fog on the adiabatic.
Trying to ascertain suitability of a 6mm bonding conductor in a domestic installation. Doesn't help that I forgot my regs book too!

I have a pefc of 1.17KA. Can anyone help please?

Thanks.
 
Quiet this morning!
My thoughts were that if I could prove minimum size of the main installation earthing conductor and then use the 50% rule for the main bonding conductor it might come out at <6mm. Although I have just noticed that the installation has TNCS earthing! Does this mean I can't calculate and have to select from table??

Any help please?
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
on a TNC-S installation min. size for bonding conductors is 10mm.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
We're doing remedials at this installation, including a consumer unit upgrade. The route for rewiring the bonding conductor is unbelievably difficult! Is there any way I can risk assess to get around rewiring this 6mm bonding conductor? ?
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...

I think you are talking about the test to prove whether an item is an extraneous part or not.
 
main bonding protective conductors are sized by the Relevant table in the IEE REGS, not by adiabactic equation.
i just use whatever i find first on the van. still got a roll of plain green. (imperial). think it still has the price on the 100 yard drum.... ÂŁ1.10.,6d.
 

Reply to Adiabatic equation help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
659

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top