Now I know this has probably been covered a few times but I'm struggling to come to terms with my own calculations.
I would appreciate it if someone could tell me if my calculations are correct.
So basically I've done a periodic and some of the CPC sizes for sub mains are less than half the size of the live conductors. I have gone through what I think is the correct procedure for the adiabatic equation and it is telling me that for a 200A TP+N supply the CPC can be 2.5mm, the live conductor is 95mm so I find this rather unrealistic.
This is what I have worked out:
S = square root of (l squared x t) / k
Now I have the Zs reading of the circuit which is 0.10 ohms.
So: 230 / 0.10 = 2300A (fault current)
Times this by itself: 2300 x 2300 = 5,290,000
Now I've got the schneider mccb tripping curves from here:-
http://www2.schneider-electric.com/...AQS/166000/FA166316/en_US/Tripping_Curves.pdf
So as it is a 200A MCCB (TM200D) of this range and the pfc was 2300A : 2300 / 200 = 115
Then according to the graph, anything over about 24A is <0.01 seconds (10 milliseconds).
The formula now looks like : S = square root of (5,290,000 x 0.01) / k
Then : S = square root of (52,900) / k
Then : S = 230 / k
As it is a separate earth cable run alongside the SWA I have applied the k factor of 143.
So : S = 230 / 143 = 1.6
Next size of cable up is 2.5mm.......... Surely not!
I would appreciate it if someone could tell me if my calculations are correct.
So basically I've done a periodic and some of the CPC sizes for sub mains are less than half the size of the live conductors. I have gone through what I think is the correct procedure for the adiabatic equation and it is telling me that for a 200A TP+N supply the CPC can be 2.5mm, the live conductor is 95mm so I find this rather unrealistic.
This is what I have worked out:
S = square root of (l squared x t) / k
Now I have the Zs reading of the circuit which is 0.10 ohms.
So: 230 / 0.10 = 2300A (fault current)
Times this by itself: 2300 x 2300 = 5,290,000
Now I've got the schneider mccb tripping curves from here:-
http://www2.schneider-electric.com/...AQS/166000/FA166316/en_US/Tripping_Curves.pdf
So as it is a 200A MCCB (TM200D) of this range and the pfc was 2300A : 2300 / 200 = 115
Then according to the graph, anything over about 24A is <0.01 seconds (10 milliseconds).
The formula now looks like : S = square root of (5,290,000 x 0.01) / k
Then : S = square root of (52,900) / k
Then : S = 230 / k
As it is a separate earth cable run alongside the SWA I have applied the k factor of 143.
So : S = 230 / 143 = 1.6
Next size of cable up is 2.5mm.......... Surely not!