Hi Guys my question is with relation to the adiabatic equation, I am aware that the following is true.

S = Size of earth bonding conductor required.
I = pfc in amps.
t = disconnection time in seconds.
K = values in table 43.1.

If I am trying to work out if a 6mm gas and water bond is adequate on a TN-C-S system where in the regs do I find the following.

1. disconnection time (I presume it is for the main incomer fuse) which in this case is 80 amp BS1361.
2. What cable am I wanting the K value for and how do I find its characteristics if it was not installed by me.

Any help appreciated guys :)

If someone could do a working calculation it would be fantastic. pfc on this job is 2.4 KA.

Just to add I always upgrade the gas and water bonds if I am asked to change a consumer unit but in this case it is almost impossible without major disruption which the customer wants to avoid.

Also am I right in thinking that if it was a TN-S system then I would have to upgrade the gas and water earths to 10mm.
 
Hi there.

You're right but you've got it mixed up....as you have a TN-C-S system, all main bonding conductors must be 10mm.

For TN-S you can use the adiabatic to check conformity of a 6mm bonding conductor by confirming the minimum CSA of main protective conductor.



EDIT.....Works out at about 6.5mm.;)
 
Last edited by a moderator:
Thanks Lenny

But on a consumer unit change am I right in thinking the gas and water earth being 6mm would only gain a recommendation code 4 if there are no signs of deterioration of the insulation, and therefore I can happily perform the consumer unit change if all else is fine.

Also I would appreciate it if you could lead me in the right direction for the adiabatic please. :)
 
I squared you have there.


(T) comes from APP 3 of ol red. (K) comes from table 43.1 of ol red. (S) must be equal to or greater than the result of the sum.

(S) = the square root of ((I) squared x (T)) divide by (K).



2400 x 2400 = 5760000

5760000 x 0.1 = 576000

Square root of 576000 = 758.9

758.9 / 115 = 6.59mm
 
Last edited by a moderator:
2400 x 2400 = 5760000

5760000 x 0.1 = 576000

Square root of 576000 = 758.9

758.9 / 115 = 6.59mm


Hmmmmmmmm

ermmmmmmm

mmmmmmmm

Hmmmmmmmmmmmmmm

Hmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmm

Erm Lenny, mmmmmmmmm

Hmmmmmmmmmmmm

Lenny,

Hate to ask thissssssssssssss ...........

but was it you who nicked my calculator? :D
 
Thanks again fellas:confused:

But with regards to a consumer unit change can it be performed if the gas and water earths are left at 6mm but the main earth is upgraded to 16mm ? There are mitigating circumstances due to disturbance that would be caused.

PS how did you arrive at the K factor and disconnection time please.

Thanks again.

I see the tables you noted Lenny but is the cable K factor for the Electric board supply cable or tails?
 
Last edited by a moderator:
The K factor is for the bonding cable i.e 70 degrees c thermoplastic, copper conductor, less than 300mm CSA.

Disconnection time is from the time/current graphs in appendix 3.
 
Thanks guys it finally hits home :D

What would be your feelings on changing the consumer unit if the gas and water earths were not changed ? Could it be done with a recommendation code 4 as it must have been fit for purpose when installed.
 
I squared you have there.


(T) comes from APP 3 of ol red. (K) comes from table 43.1 of ol red. (S) must be equal to or greater than the result of the sum.

(S) = the square root of ((I) squared x (T)) divide by (K).



2400 x 2400 = 5760000

5760000 x 0.1 = 576000

Square root of 576000 = 758.9

758.9 / 115 = 6.59mm

That's the main earthing conductor, the bonding conductors have to be at least 1/2 this and a minimum of 6mm, so his 6mm gas and water bonding is fine if t-n-s.
 
Thanks guys it finally hits home :D

What would be your feelings on changing the consumer unit if the gas and water earths were not changed ? Could it be done with a recommendation code 4 as it must have been fit for purpose when installed.


If changing the consumer unit then it is needs a EIC so where can you put a code 4 on a EIC?
 
I thought I could put the note in comments on existing installation on the almost bottom right of page 1.

Does anyone else have a view on the 6mm gas and water earths being left as they were fit for purpose on installation, and surely I would be improving the installation?

I spoke to the NICEIC tech helpline today about the matter and the guy on there asked me why I was carrying out a PIR for a consumer unit change so I had to give him advice can you believe. :eek:

PS The supply characteristic is TN-C-S Andy so with this in mind are your thoughts the same mate ?
 
Last edited by a moderator:
That's the main earthing conductor, the bonding conductors have to be at least 1/2 this and a minimum of 6mm, so his 6mm gas and water bonding is fine if t-n-s.

Sorry, should have made that clear.:eek:

With regard to TN-C-S 6mm is too small as it states that main earthing conductors should be size for size upto 16mm and main protective bonding conductors must be a minimum of 10mm.
 

Reply to Adiabatic equation question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top