Can someone please tell me if i have done this correct.
Got a fuseboard change and the tails are 16mm sinlges fed from an 800kmf with a 6mm single main earth.
Board is other side of house to meter so a pain to upgrade main earth.
Done the adiabitic and it comes out as follows.
Supply is tnc-s with an 80amp bs 1361
So : S = Square root of I(squared) x Time divided by k factor
230/0.2 = 1150 ( I)
1150 x 1150 = 1322500 ( I squared)
1322500 x 0.2 = 264500 ( I squared x Time for 80amp fuse)
Square root = 3.59
So 6mm main earth is fine
Got a fuseboard change and the tails are 16mm sinlges fed from an 800kmf with a 6mm single main earth.
Board is other side of house to meter so a pain to upgrade main earth.
Done the adiabitic and it comes out as follows.
Supply is tnc-s with an 80amp bs 1361
So : S = Square root of I(squared) x Time divided by k factor
230/0.2 = 1150 ( I)
1150 x 1150 = 1322500 ( I squared)
1322500 x 0.2 = 264500 ( I squared x Time for 80amp fuse)
Square root = 3.59
So 6mm main earth is fine