Can someone please tell me if i have done this correct.
Got a fuseboard change and the tails are 16mm sinlges fed from an 800kmf with a 6mm single main earth.

Board is other side of house to meter so a pain to upgrade main earth.

Done the adiabitic and it comes out as follows.

Supply is tnc-s with an 80amp bs 1361


So : S = Square root of I(squared) x Time divided by k factor

230/0.2 = 1150 ( I)

1150 x 1150 = 1322500 ( I squared)

1322500 x 0.2 = 264500 ( I squared x Time for 80amp fuse)

Square root = 3.59

So 6mm main earth is fine
 
gas is at the met water is from the db will be installing 10mm bonds from met to gas and water
 
just read the post below so i think i will run the 10mm bonds from the met in the meter cupboard and the 6mm cpc for the db leave in place
 
Can someone please tell me if i have done this correct.
Got a fuseboard change and the tails are 16mm sinlges fed from an 800kmf with a 6mm single main earth.

Board is other side of house to meter so a pain to upgrade main earth.

Done the adiabitic and it comes out as follows.

Supply is tnc-s with an 80amp bs 1361


So : S = Square root of I(squared) x Time divided by k factor

230/0.2 = 1150 ( I)

1150 x 1150 = 1322500 ( I squared)

1322500 x 0.2 = 264500 ( I squared x Time for 80amp fuse)

Square root = 3.59

So 6mm main earth is fine

Sorry don't follow your calc at all - k(for copper) usually 115

but anyway, if it is a tn-c-s the earthing conductor should be at least 16 mm and the protective bonding conductor should be at least 10mm (see table 54.8 BRB)
 
Hi,
I think the adiabatic equation is for cpc cross sectional areas (csa's) in a circuit.

It does not apply to the cpc csa for main protective or bonding conductors.

You should use 16mm main earth and 10mm for gas/water

Sav
 
Last edited by a moderator:
yeh adiabatic is for cpc's mate, and you will have to up grade the tails to 25mm2(obviously) as well as the earthing conductor to 16mm2, the gas and water can be 10mm2.....
 
I dont agree with you on that.
Where in the regs does it say that the main earth should be 16mm for tnc-s supply?
It says that you can use either calculation or the table to choose the size for any earth except main bonds.
If i run the main bonds back to the incoming met then dont see a problem.
And yes sorry used the wrong k factor so comes out at 4.7 mm
 
I dont agree with you on that.
Where in the regs does it say that the main earth should be 16mm for tnc-s supply?
It says that you can use either calculation or the table to choose the size for any earth except main bonds.
If i run the main bonds back to the incoming met then dont see a problem.
And yes sorry used the wrong k factor so comes out at 4.7 mm

Reg 544.1.1 leads you to table 54.8 which tells you the minimum size of a main protective bonding conductor for a tn-c-s is 10mm.

with regard to the earthing conductor i think it is more a usual requirement of the distributor wanting a minimum size for both tn-s and tn-c-s. The OSG page 28, note 2 tells you this .

Hope this helps.
 
Can someone please tell me if i have done this correct.
Got a fuseboard change and the tails are 16mm sinlges fed from an 800kmf with a 6mm single main earth.

Board is other side of house to meter so a pain to upgrade main earth.

Done the adiabitic and it comes out as follows.

Supply is tnc-s with an 80amp bs 1361


So : S = Square root of I(squared) x Time divided by k factor

230/0.2 = 1150 ( I)

1150 x 1150 = 1322500 ( I squared)

1322500 x 0.2 = 264500 ( I squared x Time for 80amp fuse)

Square root = 3.59

So 6mm main earth is fine

Where did the 0.2 come from, resistance presumably but why 0.2?
 
the first 0.2 is the ze and the second one is for disconnection time of an 80amp fuse
 

Reply to adiabatic equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top