Hi All,
I think I have confused myself somehow and feel I am spiraling into further confusion. When I am doing the equation, it is saying the longer the cable is, the smaller the CPC has to be. My calculations are below.
20A radial BS61009-1 Curve C
Install method type B using 2.5 singles
Ambient 30c
Volt drop is fine (1%)
OSG table I1 = 14.82
OSG table I2 = 1.04
Length = 6.3m
14.82 x 1.04 x 6.3 / 1000 = 0.10
+ Ze 0.13 = Design Zs of 0.23
230v/0.23 Zs = 962.1A
Tripping time - 0.1s
962.1 x 962.1 = 925,636.41 x 0.1 = 92,563.64
Sqr Rt 92,563.64 = 304.24
304.24 / 115 (k) = 2.65mm
I won't show the working out but if I increase the cable length to 20m, my adiabatic answer becomes 1.37mm
I know I wouldn't design a 20A Radial using 4mm cable but I can't seem to pull myself out of this hole.
Thank you in advance for your help.