Mattdev
This one has always made me wonder !??
Does this work as simply for a 3 phase installation i.e 3.3kw over 230volts = 14.3 amps
so does 3.3kw over 400volts = 8.8amps per phase OR is it 3.3kw over 230volts divided by 3 = 4.8 amps per phase ???
Hello.
It will be Ib / square root of 3 x Ul
which will mean
3300 / (1.732... x 400) = 4.76 Amps
a factor may also need to be considered.
Reply to Adiabatic equation in the The Welcome Forum area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
M
Hi and welcome to the forum. Thanks for posting. I'll stay out of the advice because I'm not a sparky. But welcome aboard and if you need anything...