Evening All,
I have an industrial install this week, installing 200A feeds to MCCB panels in workshop, with 70mm SWA
Im just working out the CPC at the DB, not done this for a while so just wanted to check it..
S= root(I2 X T) / K
The fuses are BS88-2 200A, i have another DB in exactly the same place with same sized cable, and the ZS is 0.04 PFC 5.2KA
so using those figures-
Root ((5200x5200)X0.1= 1644.38/ 115= 14.2mm
So 16mm will be adequate. does this look correct?
Reply to Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...