B

beaver74

Hi all have tested a flat were the main bond is only 6mm
the incomer is 1361 60A
main earthing conductor is 16.oomm

doing the adiabatic calculation what disconnection time would i use to assess if this conductor is man enough (and yes i know it should be 10.00 but the customer want have any work done so i want to report to him and sleep at night.

on the same theme what disconnection time would you use generally 0.4 0.1
 
Have a read of reg 543.1.3 which states that the time is the operating time of the disconnecting device corresponding to the fault current.

Then check table in appendix 3.
 
You cant use the adiabatic to size bonding conductors........It depends on the earthing system present and condition of the conductor itself as to wether 6mm is still sufficient tor not.;)
 
Where PME conditions do not apply, Regulation 544.1.1 requires a main bonding conductor to have a csa not less than half the csa for the earthing conductor of the installation and not less than 6 mm2.

Where PME conditions apply, Regulation 544.1.1 requires the main bonding conductors to be selected in accordance with the neutral conductor of the supply and Table 54.8H.

Regards

Dichroic
 
I missed the bit about main bond and presumed the op was talking about the Main earthing Conductor.:mad:
 
Just to be clear, you are on a pme system or otherwise known as a TN-C-S system. When using table 54.8 in the regs it is referring to the size of the neutral conductor inside the armoured cable of the supply cable NOT the size of the neutral conductor of the 25mm tails on the consumers side:


It is important to appreciate that the ‘supply neutral conductor’ referred to in Table 54.8 of the regulations is the neutral conductor of the electricity distributor’s low voltage network (otherwise known as the combined protective and neutral (PEN) conductor). It is not the neutral conductor on the consumer’s side of the supply terminals, which may have a smaller csa.

Many people think that this table is referring to the size of the "tails" neutral conductor.

Regards

Dichroic.
 
If the MPB is not being upgraded it is essential to check out the connection at the Clamp to ensure circulating currents have not caused overheating..then make comment on it on the P.I.R as code 4.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
adiabatic test of mian bond
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
beaver74,
Last reply from
sparkylad,
Replies
8
Views
1,883

Advert

Back
Top