Hi all, I am new to this forum so apologies if this topic has been covered before!
Basically, I have been asked to test a commercial installation that is approx 2 years old however the original electrical contractor have gone bust. On reviewing the certificates I noticed that while 95% of the readings are correct there are about 40 circuits where the measured Ze exceeds the maximum permitted for the protection device installed, some are Type C RCBO’s and some are Type C Breakers. I know that they would pass if I changed all of them to Type B RCBO’s but this will be an expensive exercise.
Regarding the circuits protected by RCBO’s, I understand the RCBO still provides protection against shock risk in line with 411.4.9 and Table 41.5 but does not prove overcurrent protection in line with Chapter 43. I need to establish the L-L or L-N conductors are being protected against thermal damage under overcurrent conditions.
I think I can do this by showing that they pass the adiabatic test. It is a long time since my C course days and I cannot remember or find out how to do this therefore any assistance would be greatly appreciated.
If I can prove the circuits protected by RCBO pass the adiabatic test I intend to leave them and change the few circuits that are protected by the C Type MCB to a RCBO B Type.
Basically, I have been asked to test a commercial installation that is approx 2 years old however the original electrical contractor have gone bust. On reviewing the certificates I noticed that while 95% of the readings are correct there are about 40 circuits where the measured Ze exceeds the maximum permitted for the protection device installed, some are Type C RCBO’s and some are Type C Breakers. I know that they would pass if I changed all of them to Type B RCBO’s but this will be an expensive exercise.
Regarding the circuits protected by RCBO’s, I understand the RCBO still provides protection against shock risk in line with 411.4.9 and Table 41.5 but does not prove overcurrent protection in line with Chapter 43. I need to establish the L-L or L-N conductors are being protected against thermal damage under overcurrent conditions.
I think I can do this by showing that they pass the adiabatic test. It is a long time since my C course days and I cannot remember or find out how to do this therefore any assistance would be greatly appreciated.
If I can prove the circuits protected by RCBO pass the adiabatic test I intend to leave them and change the few circuits that are protected by the C Type MCB to a RCBO B Type.