Applied for 4kW PV to Western Power for a location at the end of the line in the sticks on a small transformer with 3 houses on it. They took a week to reply (which is not bad) but the answer was no way at 4kW, way outside what the network will take. Rough cost estimate to reinforce network was ÂŁ3K to ÂŁ5K to recable using ABC, possibly with transformer change as well. But I can connect at 3.7kW (16A) no problem! In engineering terms it is difficult to see how 4kW is impossible but 3.7kW is OK, particularly as I measured the voltage there today as 251V, which at 16A would be just over 4kW!
On a related point I feel SMA is missing a gap in the market here for an inverter at 3.7kW limited to 16A output. Power one do a twin mppt transformerless (Aurora) at 3.6kW size. With a bit of firmware adjustment the SMA 4000TL could sit there nicely. The advantage of SMA is that it has bluetooth.
Does anyone know whether the parameters of the 4000TL can be adjusted with an installer password to bring it within the 16A limit?
Regards
Bruce