I'm going to throw a swerve ball in this; if I'm reading and understanding the OP correctly then he's talking about taking the feed from the meter, splitting it, one goes to house via tails and one goes to barn via a KMF. Divorced earth at the barn end and the armour for the SWA only glanded at that end as well.

Personally, can't see any big issues with that. BGB doesn't say WHERE an armour has to be earthed, just it does. The swa becomes a 5s circuit anyway as it's not a final.

That' exactly what I'm talking about!
I was lying awake in bed last night and I couldn't think of any good reason why the armour has to be earthed at the supply side. In reality, earthing (via MET) to a rod on the supply side, or eathing (via MET) to a rod at the barn - and the two rods are less than 4ft away from each other!
 
That' exactly the two rods are less than 4ft away from each other!

That's the only thing I'd raise an eyebrow to, as they will interfere with each other. See if you can get them further apart.
 
That's the only thing I'd raise an eyebrow to, as they will interfere with each other. See if you can get them further apart.

Hmm. Not considered that. Clients are quite specific about what they do an don't like so the location of the new rod was decided by them. If there'd been any choice in the matter I'd have run some new armour clipped to the underside of a raised step across the path straight into the meter box - but that apparently wasn't acceptable aesthetically.....

Anyhoo.
How far apart would they need to be?
 
How far apart would they need to be?

Ooh....that's a good question! Off the top of my head I'd say greater than 3xdepth of rod, but happy to be corrected! Nowhere near a BGB all day.
 
Given the likely Ra of the TT earthing (existing or new), don't you need to put an RCD (100mA, type S?) at the supply end of the distribution circuit to provide protection in the event of an earth fault?

I'd be inclined to put a new rod in for the outbuilding, but connect the SWA armour at both ends, so that you end up with multiple rods for the whole installation. I don't see a need to separate the earthing of the two parts of the system.
 
Given the likely Ra of the TT earthing (existing or new), don't you need to put an RCD (100mA, type S?) at the supply end of the distribution circuit to provide protection in the event of an earth fault?

I'd be inclined to put a new rod in for the outbuilding, but connect the SWA armour at both ends, so that you end up with multiple rods for the whole installation. I don't see a need to separate the earthing of the two parts of the system.

Wasn't the issue to do with it only being a 2c armoured which might not have sufficient csa to satisfy bonding requirements? And if the whole install is on RCBO I can't see what benefit is achieved by adding a 100mA at the upfront end when all it's protecting is one set of internal tails installed in a non-vulnerable method and an armoured cable.
 
Wasn't the issue to do with it only being a 2c armoured which might not have sufficient csa to satisfy bonding requirements? And if the whole install is on RCBO I can't see what benefit is achieved by adding a 100mA at the upfront end when all it's protecting is one set of internal tails installed in a non-vulnerable method and an armoured cable.

OK, maybe it's an unlikely fault, but if the SWA is damaged and the line becomes connected to the armour, what provides disconnection in the time required (1 second for a TT distribution circuit) if it's not covered by an RCD? The cartridge fuse in the KMF won't blow in the required time due to the low earth fault current on a typical TT installation. See 411.3.2.1 and 411.3.2.4
 
OK, maybe it's an unlikely fault, but if the SWA is damaged and the line becomes connected to the armour, what provides disconnection in the time required (1 second for a TT distribution circuit) if it's not covered by an RCD? The cartridge fuse in the KMF won't blow in the required time due to the low earth fault current on a typical TT installation. See 411.3.2.1 and 411.3.2.4

A valid point and one that I actually included then deleted out again on an earlier post as I didn't want to muddy the waters! We usually adhere to the convention that an armoured cable does not require RCD protection - and in this case it seems incredibly unlikely that anyone is ever going to stick a digger bucket through it, either! OK, so add another ££ onto the job and fit an upstream 100mA S type, just for peace of mind. Now, how often do you think that RCD will get routinely tested?
 

Reply to Advice for providing power to a barn conversion in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
768
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Yeh im unsure without a photo of external box.
Replies
4
Views
268

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top