Going back to the question of which end of the SWA should be earthed.
Regulation 542.1.3.3 requires it to be earthed at the installation containing the protective device. In this case the house end of the cable.
Obviously the other option is to connect at both ends.
 
Hmm. Not considered that. Clients are quite specific about what they do an don't like so the location of the new rod was decided by them. If there'd been any choice in the matter I'd have run some new armour clipped to the underside of a raised step across the path straight into the meter box - but that apparently wasn't acceptable aesthetically.....

Anyhoo.
How far apart would they need to be?


Amazing you're actually listening to the clients, that know absolutely nothing about TT systems, and even less than you seem to know, and allowing them to dictate where the earth electrodes are going to be positioned!!!! Who is the paid professional them or You? .... I'm Gobsmacked!!

Get them as far apart as possible, at least 1.5 to 2 X the buried depth. So what are you going to or thinking about bashing in then, ....3/8'' twiggs (eg 1.2m), or a couple 5/8'' coupled together (eg 2.4m depth)??


Not going to go any further, just going to watch and see what happens on this thread...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice for providing power to a barn conversion
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
The General,
Last reply from
Engineer54,
Replies
31
Views
6,247

Advert

TrueNAS JBOD Storage Server

Back
Top