Going back to the question of which end of the SWA should be earthed.
Regulation 542.1.3.3 requires it to be earthed at the installation containing the protective device. In this case the house end of the cable.
Obviously the other option is to connect at both ends.
 
Hmm. Not considered that. Clients are quite specific about what they do an don't like so the location of the new rod was decided by them. If there'd been any choice in the matter I'd have run some new armour clipped to the underside of a raised step across the path straight into the meter box - but that apparently wasn't acceptable aesthetically.....

Anyhoo.
How far apart would they need to be?


Amazing you're actually listening to the clients, that know absolutely nothing about TT systems, and even less than you seem to know, and allowing them to dictate where the earth electrodes are going to be positioned!!!! Who is the paid professional them or You? .... I'm Gobsmacked!!

Get them as far apart as possible, at least 1.5 to 2 X the buried depth. So what are you going to or thinking about bashing in then, ....3/8'' twiggs (eg 1.2m), or a couple 5/8'' coupled together (eg 2.4m depth)??


Not going to go any further, just going to watch and see what happens on this thread...
 

Reply to Advice for providing power to a barn conversion in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
768
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Yeh im unsure without a photo of external box.
Replies
4
Views
268

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top