Called out today for an electrical fault.. Lights tripped and wouldn't reset (downstairs lights)
Checked consumer board and found mcb (non rcd) had been reset by client and no power in lighting circuit..
Quick check and no power to top of mcb.. diagnosise mcb blown..
Mcb blown means short circuit somewhere or overloading..
6 amp mcb to lighting circuit/s.. 2 cables.. running both upstairs and downstairs lighting circuits.
Consumer unit changed.friend of a friend etc.... spare 6 amp mcb next to lighting circuit..
No seperation of circuits?..more unanswered questions...
Dismantle cables to circuits. 2 line 2 neutral and 1 earth... another question
r1 and r2 of circuits.. getting readings of continuity downstairs.. both lines together and earth..
split lines to seperate circuits.... line 1 power & line 2 power.. End to end line to line continuous.. end to end neutral no reading.. .Diagnosise circuits are joined somewhere....
Kitchen light 3 feeds going in and 1 switch wire... lounge 2 dimmer switches/2 lights 400 amps ( signs of overheating to live feeds )..hallway fine. Upstairs landing 3 feeds and 1 switch wire..bedroom 1 ok... bedroom 1 not checked ( ceiling light and fan ) bedroom 2 not checked.... bedroom 3 ok.. visuals
Got to insulation resistance test all cables to see if there is a break in insulation...Once i can determine whats going where and what to.( dont want to fire 500v into somethinguntil i can diagnose cable runs and equipment)
Short of dismantling everything within the cable areas and testing Insulation resistance as a whole on both circuits, then breaking down into individual runs of cable when problems pop up... is there any other way to diagnose this problem?
Checked consumer board and found mcb (non rcd) had been reset by client and no power in lighting circuit..
Quick check and no power to top of mcb.. diagnosise mcb blown..
Mcb blown means short circuit somewhere or overloading..
6 amp mcb to lighting circuit/s.. 2 cables.. running both upstairs and downstairs lighting circuits.
Consumer unit changed.friend of a friend etc.... spare 6 amp mcb next to lighting circuit..
No seperation of circuits?..more unanswered questions...
Dismantle cables to circuits. 2 line 2 neutral and 1 earth... another question
r1 and r2 of circuits.. getting readings of continuity downstairs.. both lines together and earth..
split lines to seperate circuits.... line 1 power & line 2 power.. End to end line to line continuous.. end to end neutral no reading.. .Diagnosise circuits are joined somewhere....
Kitchen light 3 feeds going in and 1 switch wire... lounge 2 dimmer switches/2 lights 400 amps ( signs of overheating to live feeds )..hallway fine. Upstairs landing 3 feeds and 1 switch wire..bedroom 1 ok... bedroom 1 not checked ( ceiling light and fan ) bedroom 2 not checked.... bedroom 3 ok.. visuals
Got to insulation resistance test all cables to see if there is a break in insulation...Once i can determine whats going where and what to.( dont want to fire 500v into somethinguntil i can diagnose cable runs and equipment)
Short of dismantling everything within the cable areas and testing Insulation resistance as a whole on both circuits, then breaking down into individual runs of cable when problems pop up... is there any other way to diagnose this problem?