the-moog

Advice on this installation please.

The existing house wiring is single phase to an internal consumer unit, with incomming 3 phase on PME in an external box which also contains the isolator which is 4 pole.

i.e.
Incomming (3Ph) - Main Fuse (3Ph PME) - meter (3Ph) - isolator (4 pole 3Ph) - tails - CU (1Ph)

This external 4 pole isolator is to be connected to the garage which requires 3 phase. In the garage there is a new distribution board. As well as a mix of single and three phase equipment, the garage also supplies external lighting pond pumps etc on single phase with the required RCDs.

So, question 1 is; should the isolator on the garage dist board be 3 pole or 4 pole, remembering that the systems is PME?

Logic tells me 3 pole so equipment metalwork still has earth continuity when the main isolator is on and the garage isolator is off.

Question 2 is; should the garage have an earth rod?
 
So, question 1 is; should the isolator on the garage dist board be 3 pole or 4 pole, remembering that the systems is PME?

Reg 537.2.1.1 says in a TNCS or TNS it only has to be 3 pole.

Question 2 is; should the garage have an earth rod?

Is the garage part of the main building or separate? If it is separate, how far away is it? How are you going to get the supply to the garage? Are there any extraneous/exposed conductive parts in the garage?
 
Last edited by a moderator:

Reply to Advice: Mix of 1 and 3 phase on PME in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
629
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
479

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top