Hi all
Recently changed a consumer unit , adding new radial, bonding etc for my initial assessment, IR tested everything initially and before been terminated in new board, all readings ok.
I'm sure I've read that if it is a new installation that the board as a whole need testing?

My question is how can you test the whole installation when it is a wylex split board with 2 rcd's as the 500v could damage them?

Thanks in advance for your comments
 
Hi all
Recently changed a consumer unit , adding new radial, bonding etc for my initial assessment, IR tested everything initially and before been terminated in new board, all readings ok.
I'm sure I've read that if it is a new installation that the board as a whole need testing?

My question is how can you test the whole installation when it is a wylex split board with 2 rcd's as the 500v could damage them?

Thanks in advance for your comments

Always been told, (and agree with), that IR testing is done after termination of all conductors, accessories screwed on etc. etc.

You might damage or tighten down on a conductor when terminating and you wouldn't know.:)

As for the testing,

If you don't want to by-pass RCDs and test whole board,

Loads removed, MCBs off, outgoing side of each MCB to neutral bar/s and then to earth bar/s. Test between neutral bar/s and earth bar/s. Job done.
 

Reply to Advice needed; insulation resistance test on dual rcd board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top