Hi, just looking to bounce a few ideas together off people about an install im specing up please?
Install is a 3 phase supply for a cleaning company with industrial machines.
1 x 3PH washer 12kw 32A per phase.
1 x 3PH washer 18kw 45A per phase.
2 x dryers 40A per phase.
2 x 2 gang sockets in washer area.
Equipment is going is going to be located around 30 meters from distribution point. So was looking at installing a sub main nearer the equipment, so from the main DB in 10mm swa 4 core and then from the sub-main in 4mm swa 4 core to associated isolators.
Was wondering for the 10mm if the armour alone is enough for CPC or would need to carry a ajourning CPC? and the correct cable selection being used for the current capacity?
Any feedback appreciated, cheers.