Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point.
Supply is a standard Single Phase and I have appointments booked with my supplier and DNO to upgrade meter tails and cutout fuse respectively.
I'll get a spark to do all the connections but looking to run the cable myself to save a few ££.
In terms of the cable it looks like I have a few options so just looking for advice. The run is 28m and will be clipped direct under kitchen cabinets before exiting the exterior wall and going up and over a side extention to our driveway clipped to the exterior brickwork.
Chargepoint specs are:
A quick look at a voltage drop calculator shows me that 4mm would within range
So my choices are (with prices):
Is there any reason to consider oversizing the cable to 6mm or 10mm?
If money was not an object (it clearly is) does EV Ultra give me anything other than convenience?
Would the regs allow me to use PVC Tuff-Sheathed clipped to an exterior wall or does it have to be armoured?
- Rated power: Up to 7.2kW
- Charging current: 6A to 32A (variable)
- Rated current: Up to 32A max
- Nominal supply: 230VAC 50Hz
- Supply connections: L1, N, PE 2.5 - 10mm2
- Internet connection: Home Wi-Fi (2.4GHZ only) or a CAT5 Ethernet cable to Home LAN (Ethernet-USB Adaptor required)
Required Cable Size | 4mm |
Voltage Drop | 8.77 Volts |
Percentage Drop | 3.8% |
Current Load | 31.3 Amps |
Max Cable Load | 42.0 Amps |
- EV Ultra Cable - PVC Tuff-Sheathed - £164.64
- EV Ultra Cable - SWA Cable 3 Core - £188.16
- Seperate 4mm SWA + Shielded outdoor CAT6 - £101.51
- TL;DR
- Does EV Ultra cable offer any benefits other than convenience?