Just after thoughts and advice please.
I was asked by a customer my thoughts on a situation within some flats they own where there are single ovens (2kw load) wired directly to the electric hob above (5.5kw load) protected by 32amp mcb
They are wanting to replace the ovens (like for like) and I advised that the hobs were to stay wired on the 32amp dedicated circuit but a socket/spur to be installed so the ovens can be fused at 13 amp as per manufacturers instructions and to avoid overload on 32 amp circuit with hob and oven on full load and also maybe possible overcurrent risk,
I suppose diversity should be taken into account so maybe not much risk of overload.
I am debating with myself whether or not this extra work does need to be done and would like any reasons for and against if poss.
Obviously if this was a new install I wouldn't have designed it in this way but this is existing and would like to weigh up reasons for and against installing supply via 13 amp fuse for oven, also don't want to give client wrong advice if this is the case.
I just feel that on one hand although not fused at 13 amp there is local isolation available but on the other hand I would always try to use protection as near as poss to the power rating of the appliance.
Am I right in thinking that for example a loose termination on the oven wouldn't be an issue with causing the fuse to blow as this causes s higher resistance and less current to flow? Or would this possible fault increase the current and therefore be a fire hazard as the oven wiring would overheat before tripping 32amp mcb?
Just trying to think of all possible outcomes for these two scenarios.


Thanks in advance.
 
Any standard cooker / oven /hob circuit will be a 32A radial so manufacturers should really be aware of this and design their equipment accordingly.
If the oven is supplied with a plug and the manufacturers instructions indicate that this fusing is required then the provision of a socket instead of the hard wiring would be a good idea.
The overload scenario has been down to death and whilst it may be possible it is very unlikely.
The fault protection is the key issue, is the oven suitably protected with a 32A MCB for fault protection?
I would say probably as the disconnection on full fault current would be likely to be sufficiently quick to not require a larger cpc. However the individual circumstances of the circuit should be checked to confirm this.
 

Reply to advice on cooker wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
217
  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
1K
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
786
First thing to say is that it's desirable to have a method of isolation for the oven somewhere near it in the kitchen, and not hidden behind a...
Replies
1
Views
1K
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
582

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks