Hi,

I am after some advice,

I am having an extension build to my dining room, I have a modern house, 2007 and I want to install the electrics myself. I am a skilled enough person have good knowledge of electric wiring, safety etc.

I questions are basically to check if there is anything new or different I have to do in order to comply with any new regs, etc. I fairly confident the work does not need to be covered under part p, but as part of the building consent for the extension the details of this work have been roughly covered in the original plans sent to building control.

My plans are to extend the current lighting and ring main circuits, basically I want to add a new light fitting to the existing dining room lighting circuit, so it runs off the same switched circuit, I will use 1 run of cable to supply the neutral and switched live from the existing light fitting to the new one.

Then a set of LV downlights (12v 20watts max per bulb) in the ceiling, running off a transformer controlled via a normal light switch, so a new wiring leg taken off the existing lighting circuit and a new cable to the light switch for the switch control.

1.5mm twin & earth cable for the lighting.

The existing sockets are a ring main, using 2.5mm cable, so I plan to break the ring in the ceiling and add a juction box and then run 4 double sockets and then rejoin back to the ring main via another junction box.

2.5mm twin & earth for the sockets.

Any cable that runs down the walls behind plasterboard or insulation will be covered in plastic capping or trunking.

Does this sound OK,

Thanks in advance

Neil
 
Hi,

I am after some advice,

I am having an extension build to my dining room, I have a modern house, 2007 and I want to install the electrics myself. I am a skilled enough person have good knowledge of electric wiring, safety etc.

I questions are basically to check if there is anything new or different I have to do in order to comply with any new regs, etc. I fairly confident the work does not need to be covered under part p, but as part of the building consent for the extension the details of this work have been roughly covered in the original plans sent to building control.

My plans are to extend the current lighting and ring main circuits, basically I want to add a new light fitting to the existing dining room lighting circuit, so it runs off the same switched circuit, I will use 1 run of cable to supply the neutral and switched live from the existing light fitting to the new one.

Then a set of LV downlights (12v 20watts max per bulb) in the ceiling, running off a transformer controlled via a normal light switch, so a new wiring leg taken off the existing lighting circuit and a new cable to the light switch for the switch control.

1.5mm twin & earth cable for the lighting.

The existing sockets are a ring main, using 2.5mm cable, so I plan to break the ring in the ceiling and add a juction box and then run 4 double sockets and then rejoin back to the ring main via another junction box.

2.5mm twin & earth for the sockets.

Any cable that runs down the walls behind plasterboard or insulation will be covered in plastic capping or trunking.

Does this sound OK,

Thanks in advance

Neil

I don't have access to Document P right now but I'm sure extra low voltage lighting is notifiable unless using pre-assembled fittings as a pre-assembled kit.

Cables buried in walls at depths of less than 50mm must have RCD protection or earthed mechanical protection.
 
I don't have access to Document P right now but I'm sure extra low voltage lighting is notifiable unless using pre-assembled fittings as a pre-assembled kit.

Cables buried in walls at depths of less than 50mm must have RCD protection or earthed mechanical protection.

The ring main of the sockets is already on an RCD protected circuit, so this is ok, but the lighting circuits are not I don't believe. My CU is a split load with a mains switch and 1x 30ma RCD. The lighting circuits are on the normal non-RCD side.

The 12V lighting will be a kit type bought as a single unit, lights and transformer together, although if this is an issue with part P, I can swap them for a set of mains halogen downlights.

The lighting circuit, as this is not on a RCD, do I need the CU upgrading to an RCD for the lighting? If so I assume an RCBO for the lights would accomplish this to requirements?

Thanks

Neil
 
The ring main of the sockets is already on an RCD protected circuit, so this is ok, but the lighting circuits are not I don't believe. My CU is a split load with a mains switch and 1x 30ma RCD. The lighting circuits are on the normal non-RCD side.

The 12V lighting will be a kit type bought as a single unit, lights and transformer together, although if this is an issue with part P, I can swap them for a set of mains halogen downlights.

The lighting circuit, as this is not on a RCD, do I need the CU upgrading to an RCD for the lighting? If so I assume an RCBO for the lights would accomplish this to requirements?

Thanks

Neil

It will.

Check the ELV lighting requirements, I'm going from memory!
 
special installation" means an electric floor or ceiling heating system, an outdoor lighting or
electric power installation, an electricity generator, or an extra-low voltage lighting system
which is not a pre-assembled lighting set bearing the CE marking referred to in regulation 9 of
the Electrical Equipment (Safety) Regulations 1994(a);
Taken from the Part P doc

IQ was spot on about this and if they are as you say they are pre assembled in a kit you don't need to class them as a special installation.

My major concern is though the work is not notifiable it will still need to have a MEIWC issued on the extending of the circuits, which will mean testing the circuits and obtaining the results with a calibrated meter, do you pocess either either the knowledge or the meter

You will also need to insure that the Junction Box for extending the ring final is accessible for future testing or maintenance.
 
special installation" means an electric floor or ceiling heating system, an outdoor lighting or
electric power installation, an electricity generator, or an extra-low voltage lighting system
which is not a pre-assembled lighting set bearing the CE marking referred to in regulation 9 of
the Electrical Equipment (Safety) Regulations 1994(a);
Taken from the Part P doc

IQ was spot on about this and if they are as you say they are pre assembled in a kit you don't need to class them as a special installation.

My major concern is though the work is not notifiable it will still need to have a MEIWC issued on the extending of the circuits, which will mean testing the circuits and obtaining the results with a calibrated meter, do you pocess either either the knowledge or the meter

You will also need to insure that the Junction Box for extending the ring final is accessible for future testing or maintenance.

It almost stretches the reason for a Minor Electrical Installation Works Certificate even though the 'new circuit' criteria is satisfied!

I'd put the whole lot on an Electrical Installation Certificate and probably just notify it too.
 
You will also need to insure that the Junction Box for extending the ring final is accessible for future testing or maintenance.

Through crimps in a 'choc box' to enclose the connections and provide strain relief would negate the need for accessing the connections. Tend to do this a lot these days when extending ring mains or replacing damaged sections of cabling. Price is comparable material wise and the time taken to make them off isn't too dissimilar either.
 

Reply to Advice on extension wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Thanks guys, I'm going for the safe option and take your advice in getting a qualified electrician to look at it. We've inherited these issues so...
Replies
4
Views
320
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
359

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top