Currently a factory unit I am working on has 12 x 250w SON fittings exterior lights controlled via a digitel timer, photocell and contactor.
But......now they do not wont all the lighting on all through the night(only at home time and in the morning) and have asked for alternate ways of switching the lighting. They have also mentioned that sometimes they have deliveries, contractors calling in the night and so if the lights are off then a system in place so as the lighting can be switched on for a selected amount of time.
Any ideas would be very helpful.
Many thanks.
 
well you can ditch the photocell as you wont need it.
keep the timeclock connected and add a remote over-ride switch near to the deliveries door which can be wired directly from the contactor.
 
Keep the photo cell because the timer will be set to come on at say 4:30 in the afternoon and go off at 7:00pm when everybody has left for the day. So you will not have to adjust the time clock in the summer when it is light in the evenings. A time lag switch would work if it is set to give 15 minutes longer than a delivery would usually take.
 

Reply to Advice on exterior discharge lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top