48 X 200W = 9600W (9.6kW).
9600W/ 230V=41.7A (this is the design load/current Ib).
You must satisfy the equation Ib<In<Iz.
In being the protective device (fuse).
Iz being the lowest current carrying capacity of the conductor (this can be affected by the installation method, the conductor length and whether it is bunched with any other cables).
So with Ib being 41.7A, and the fuse being 45A or 50A, the first two parts of the equation are satisfied, all you have left to determine is the conductor carrying capacity.
10mm² T&E has a current carrying capacity of between 32A and 64A depending on installation method. 32A being where the cable is completely surrounded by thermal insulation, and 64A where the cable is fixed to a flat surface and open to the air.
Obviously we don't know the installation method, so we can't really determine the cable size.