Hi all,
I'm looking for some advice on a main supply if anyone could help please.
I'll explain the layout: supply from substation 100A fuse on 16mm 3-core SWA, armour earthed at sub end, not connected at other end. This supply feeds into four 63A MCBs, each one supplying a CU in a little apartment in the block. Each CU has a 32A ring and 6A lighting circuit. The feed cable from each 63A is 6mm T+E running through the attics under deep insulation.
It's immediately clear the 6mm T+E needs changing. Interestingly, back in 2008 I see it passed periodic inspection and testing like this.
I'm concerned about the feed from substation to apartment block as well, and want to get my facts straight before advising the site owner to get the installation upgraded. I'm not very familiar with main supplies from subs and how the supply rating is calculated. I've always noticed that the main supply is protected at less than the total load possible from the submains it feeds, so assume that diversity is applied on the assumption that it's unlikely that each apartment in a block, for instance, will be pulling maximum load and at the same time. How is this calculated for main supplies?
Also, it would appear that the 16mm SWA (buried underground) is undersized anyway as it's protected by a 100A fuse.
Any advice most welcome, thanks.
I'm looking for some advice on a main supply if anyone could help please.
I'll explain the layout: supply from substation 100A fuse on 16mm 3-core SWA, armour earthed at sub end, not connected at other end. This supply feeds into four 63A MCBs, each one supplying a CU in a little apartment in the block. Each CU has a 32A ring and 6A lighting circuit. The feed cable from each 63A is 6mm T+E running through the attics under deep insulation.
It's immediately clear the 6mm T+E needs changing. Interestingly, back in 2008 I see it passed periodic inspection and testing like this.
I'm concerned about the feed from substation to apartment block as well, and want to get my facts straight before advising the site owner to get the installation upgraded. I'm not very familiar with main supplies from subs and how the supply rating is calculated. I've always noticed that the main supply is protected at less than the total load possible from the submains it feeds, so assume that diversity is applied on the assumption that it's unlikely that each apartment in a block, for instance, will be pulling maximum load and at the same time. How is this calculated for main supplies?
Also, it would appear that the 16mm SWA (buried underground) is undersized anyway as it's protected by a 100A fuse.
Any advice most welcome, thanks.
Last edited: