abit of advice please from you wise people
cu change for assesment:
circuits&mcb
shower 40a
cooker 32a
ringx1(14 points)32a
garage 20a
immerson 16a
sockets radial(2 points)16a
sockets radal(4 ponts)16a
lights up 6a
lights down 6a
main fuse 80a
what ever way try a.using osg b.highest mcb then 40% of rest. i cant get the max demand below 80a. asked supplier(central networks via npower) to up grade to 100a fuse but they said they dont fit 100a anymore max off 80a.
help please
thanks neil
 
you tell him. 100% shower then 40% of the rest added up. when all said and done, it's unlikely that the cooker and shower will be on together with a large load on the socket circuits. if you want to get it down a bit, apply diversity to the cooker, tghat will shave about 10-14 A off.
 
done that telectrix but still over 80a
cooker has socket as well
i completly agree with what your saying just dont know how the assessor will veiw it just want no mistakes.
 
well. what i would do is to tell the assessor that you have worked it out using the 100% biggest load and 40% of the rest, but common sense tells you that this figure is higher than you anticipate, due to the fact that the circuits will not be simultaneously loaded to that extent.
 
They will fit 100a as they do on new builds, it maybe that you have the equivalent to 16mm entering the service head in which case they won't fit 100a as it's a few amps away from it current carrying capacity. So 80a will be your max
 
in that case i would enter 80A, as that is what the supply fuse is rated at. saves argument.
 
cheers murdoch
i agree it will never get near the 80a
but thought it was 100% of biggest load then 40% of rest in my case 98amps so what figure would you put in box
 
look at it this way. the supply fuse is 80A, so that's the max. demand they can have. (not allowing for short term overload of the fuse)
 

Reply to advice on max demand in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
885

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
716
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
316

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top